17-03-2009, 03:04 PM #1
Ammonia Refrigeration Systems
I have a system that requires 27 degree glycol. Would I use a 20 degree stuaration suction temperature for sizing and how can I determine the capacity in tons for two existing compressors.
-
17-03-2009, 03:14 PM #2
Re: Ammonia Refrigeration Systems
Hi Ronnie,
Welcome to the RE forums.
The use of a specific SET (saturated evaporating temperature) is one of user preference. If you need 27°F glycol you also need to verify where the compressor capacity balances with the evaporator capacity (minus suction line pressure losses, which include valves, fittings, and "regulators if used").
If we looked at the 27°F glycol temperature being provided at a 22°F SET, then we might also allow a 2° temperature loss (converted to equivalent pressure loss for piping and valves, etc.) the SST (saturated suction temperature would be 20°F. That is what you pick the compressors for.
Let's start with this and go from there.If all else fails, ask for help.
-
18-03-2009, 07:11 AM #3
Re: Ammonia Refrigeration Systems
Hello Ronnie
What is the percentage of glycol in the solution ?? and which glyycol are you using?? I hope temperatures are in deg F
-
18-03-2009, 03:33 PM #4
Similar Threads
-
contaminants in ammonia systems
By Johnny Rod in forum RefrigerantsReplies: 29Last Post: 17-10-2011, 05:26 PM -
Vrv
By tgoonter in forum Air ConditioningReplies: 4Last Post: 11-01-2011, 06:25 AM -
Technical Book on Ammonia Refrigeration
By Samarjit Sen in forum Refrigeration BooksReplies: 0Last Post: 25-04-2008, 06:14 AM -
My local Apprentice Training Classes
By shogun7 in forum TrainingReplies: 12Last Post: 17-03-2007, 03:10 PM