    I have a system that requires 27 degree glycol. Would I use a 20 degree stuaration suction temperature for sizing and how can I determine the capacity in tons for two existing compressors.




  2. #2
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: Ammonia Refrigeration Systems

    Hi Ronnie,

    Welcome to the RE forums.

    The use of a specific SET (saturated evaporating temperature) is one of user preference. If you need 27°F glycol you also need to verify where the compressor capacity balances with the evaporator capacity (minus suction line pressure losses, which include valves, fittings, and "regulators if used").

    If we looked at the 27°F glycol temperature being provided at a 22°F SET, then we might also allow a 2° temperature loss (converted to equivalent pressure loss for piping and valves, etc.) the SST (saturated suction temperature would be 20°F. That is what you pick the compressors for.

    Let's start with this and go from there.
    If all else fails, ask for help.


  3. #3
    Join Date
    Jan 2009
    Location
    INDIA
    Posts
    40
    Rep Power
    0

    Re: Ammonia Refrigeration Systems

    Hello Ronnie

    What is the percentage of glycol in the solution ?? and which glyycol are you using?? I hope temperatures are in deg F

  4. #4
    Join Date
    Oct 2008
    Location
    Colombia
    Posts
    80
    Rep Power
    16

    Re: Ammonia Refrigeration Systems

    Quote Originally Posted by Ronnie Liberati View Post
    ...¿ how can I determine the capacity in tons for two existing compressors.
    H i Ronnie:

    What brand, size, type are your compressors.

Similar Threads

  1. contaminants in ammonia systems
    By Johnny Rod in forum Refrigerants
    Replies: 29
    Last Post: 17-10-2011, 05:26 PM
  2. Vrv
    By tgoonter in forum Air Conditioning
    Replies: 4
    Last Post: 11-01-2011, 06:25 AM
  3. Technical Book on Ammonia Refrigeration
    By Samarjit Sen in forum Refrigeration Books
    Replies: 0
    Last Post: 25-04-2008, 06:14 AM
  4. My local Apprentice Training Classes
    By shogun7 in forum Training
    Replies: 12
    Last Post: 17-03-2007, 03:10 PM

Tags for this Thread

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •