    High pressure gauge



    Hi guys,
    Does anyone know where I can scource an High pressure gauge up to approx 35 bar with a lazy hand indicator fitted? The problem I have is with an Airdale CUH4 heat pump that occasionally trips, I suspect on HP, although this is very difficult to confirm as I can watch my manifold gauges and all seems ok: HP around 22 bar. I leave the gauges in place as there`s other stuff to check eleswhere on site and at sometime it will trip, there`s no fault indicator and the unit will only reset when the main isolator is turned off and back on. The manual states that this is how the HP trip is reset. This is the reasoning behind my asking for a lazy hand gauge so I can confirm an actual HP fault and not dodgy HP switch or conrol fault.
    The overload does not trip and the pump will restart ok soon after tripping so I don`t think it`s a over temp problem.
    Hope this all makes sense

    Thanks guys



  2. #2
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: High pressure gauge

    Last edited by nike123; 15-03-2009 at 08:50 AM.

  3. #3
    Join Date
    Sep 2008
    Location
    england
    Posts
    427
    Rep Power
    20

    Re: High pressure gauge

    Cheers Nike,
    The Floyd gauge is the type I`m looking for. I could go for a pressure data logger but they are a bit pricey for something I`d probably not use again for a while.
    Once again, thanks

  4. #4
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,698
    Rep Power
    46

    Re: High pressure gauge

    Hi Glenn.
    You may of tried this?
    So if you have please ignore my suggestion.
    Have you tried switching off the condenser fan supply.
    Attaching a clamp meter to the overload supply.
    Then observing whether the overload or Hp switch trips first.
    Of course you could have a tricky one where (if fitted) the mechanical switching of the hp trip is tripping the Overload.
    Alternatively slightly more long winded but have you got a second unit where you could swap the overloads over.
    To see if the fault migrates?
    Cheers Grizzly
    Last edited by Grizzly; 15-03-2009 at 07:10 PM.

  5. #5
    Join Date
    Sep 2008
    Location
    england
    Posts
    427
    Rep Power
    20

    Re: High pressure gauge

    Hi Grizzly,
    I`ll give that a try, not due to go back till later this week. I`ll let you know.
    Lots of other problems on the same site ie very bad installs of the ducting by take the money and run builders.

    Cheers,
    Glenn

  6. #6
    Join Date
    Jun 2009
    Location
    hilton head island,s.c.
    Age
    63
    Posts
    7
    Rep Power
    0

    Re: High pressure gauge

    try a good set of digital gauges with a micron sensor, they do everything

Similar Threads

  1. Capillary Tube Characteristics
    By Chef in forum Fundamentals
    Replies: 9
    Last Post: 10-03-2009, 01:03 PM
  2. Compressor loading, cooling, and range of operation.
    By Air duster in forum Fundamentals
    Replies: 10
    Last Post: 02-04-2008, 08:39 AM
  3. Benji
    By benji in forum Trouble Shooting
    Replies: 29
    Last Post: 30-01-2008, 01:25 PM
  4. fun quiz
    By Brian23 in forum New to RE
    Replies: 6
    Last Post: 02-10-2007, 10:18 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •