Results 1 to 4 of 4
  1. #1
    docgreen9's Avatar
    docgreen9 Guest

    Scotsman CS60 no ice



    Hi guys hope this is the place to put this question. I have a CS60 Scotsman that is like new. It was installed used a couple times and set up since dry.

    Upon initial startup I found the water valve stuck open so replaced that. Now it'll start, fill, pump, spray but the water doesn't get cold at all and only the first 9" of the evap is ice'n up. The rest of it is cool at best. Looks kind of weird. I have no gauges. High side is hot coming out of compressor, low side is ice'n up going into the evap other than that I'm stuck.

    Any help would be appreciated.

    Thanks.



  2. #2
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,698
    Rep Power
    46

    Re: Scotsman CS60 no ice

    Hi docgreen.
    I think you may have to call someone in to look at your unit.
    Basically without gauges to confirm system pressures.
    Diagnosis would be a nightmare!
    My Initial guess would be that the system is short of refrigerant.
    But as I say at this stage it is just a guess.
    Simply put the frost line (or amount of ice at thew evaporator) is relevant to liquid refrigerant within the evaporator.
    Grizzly

  3. #3
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,698
    Rep Power
    46

    Re: Scotsman CS60 no ice

    Doc.
    You can download the Manual of this machine from the link I have added below.
    Grizzly

    http://www.mediafire.com/?hob5c0zmn16

  4. #4
    docgreen9's Avatar
    docgreen9 Guest

    Re: Scotsman CS60 no ice

    Thanks. I already downloaded the manuals. It makes ice but it took 3 hrs to produce the first batch. The manual said it should take 20 min.

Similar Threads

  1. Scotsman DCE33 icemaker
    By skidog in forum Trouble Shooting
    Replies: 4
    Last Post: 09-04-2008, 01:14 PM
  2. Need info on the shaft seal system for scotsman
    By The MG Pony in forum Commercial
    Replies: 4
    Last Post: 17-03-2008, 02:02 AM
  3. Scotsman SCE-170 Weird Situation
    By KenInEastTX in forum Trouble Shooting
    Replies: 3
    Last Post: 12-11-2007, 01:39 AM
  4. scotsman ice-machine
    By yourxmen2910 in forum Technical Discussions
    Replies: 7
    Last Post: 28-08-2006, 10:21 AM
  5. Scotsman commercial H2O inlet valve
    By fullcourt in forum Trouble Shooting
    Replies: 9
    Last Post: 25-04-2006, 11:41 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •