    Calculating weight of refrigerant based on pipe size



    Hi, Im looking for refrigerant pipe sizing software or chart that will also give me the weight of the additional refrigerant needed based on pipe size and layout for larger commercial split systems. Any help would be appreciated.



  2. #2
    Join Date
    Jan 2009
    Location
    Earth
    Posts
    75
    Rep Power
    16

    Re: Calculating weight of refrigerant based on pipe size

    Greetings and welcome to the forum!

    maybe you can give some more information for the engineers in the forum to help you, like what kind of refrigerant you using, the pipe sizing/lenght you working with and the operating temperatures and such.

    have you tried using nomographs?

    these charts can help you trace the pipe sizing you need, depending on the system capacity and also considering pressure drop and number of fittings, DuPont has a complete piping book you can take a look at.

    DuPont refrigeration piping handbook
    http://www.rapidshare.com/files/2088...dbook.pdf.html

    you can also try to use CoolPack.
    http://www.et.web.mek.dtu.dk/Coolpack/UK/index.html



    hope this helps

    regards

  3. #3
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,192
    Rep Power
    60

    Re: Calculating weight of refrigerant based on pipe size

    Most manufacturers will detail the extra weight of refrigerant required per metre/foot extra to the basic charge.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  4. #4
    Join Date
    Aug 2001
    Location
    UK
    Posts
    1,058
    Rep Power
    24

    Re: Calculating weight of refrigerant based on pipe size

    .





    Your tag says that you are in the USA, but in Europe it is a legal requirement to check certain systems regularly for leakage. This is part of the 'F Gas' Regulations that we mention from time to time. You may find some calculation tools we have for this useful.

    The leakage test frequency is dependent on the size of the system and containment weight of refrigerant. In order to determine an approximate containment quantity, the UK Govt. have sponsored a help desk (F Gas Support) and have a user's help page on the DEFRA web site. There is a set of calculation tools there intended for system owners to estimate gas quantities. Ignore the regulatory information, as it applies to the UK and the EU only - it's the calculator core information that you can adapt.

    http://www.defra.gov.uk/environment/...y/quantity.htm

    Read the PDF guidance sheet, then you can probably adapt the excel calculators for your own use.

    It assumes that you already have a system in place and know the pipe and vessel sizes.

    Nominal design pipe sizes can be obtained elsewhere or calculated. Larger systems may contain an indeterminate quantity that can only be assessed practically at site.




    .
    Last edited by Argus; 14-03-2009 at 12:55 PM.

  5. #5
    Join Date
    Mar 2009
    Location
    UKRAINE
    Age
    69
    Posts
    7
    Rep Power
    0

    Re: Calculating weight of refrigerant based on pipe size

    Quote Originally Posted by sheet59 View Post
    Any help would be appreciated.
    1) LineSize TechniSolve- Quick refrigerant line size calculations. The Refrigerant LineSize program has been developed to allow the system designer to do a quick and accurate refrigerant line sizing with very little effort.
    2) *****- The program for calculation of necessary quantity of a coolant for refuelling of refrigerating systems .

  6. #6
    Join Date
    Dec 2008
    Location
    UAE
    Age
    42
    Posts
    171
    Rep Power
    16

    Re: Calculating weight of refrigerant based on pipe size

    Dear Krio,

    I am not able to download the LineSize TechniSolve and *****, please send me

    Moderator's note: Please use the PM facility


    Your help will be appriciated.

    Thanks
    Amit
    Last edited by Argus; 15-03-2009 at 11:27 AM.

  7. #7
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,175
    Blog Entries
    6
    Rep Power
    36

    Re: Calculating weight of refrigerant based on pipe size

    Quote Originally Posted by amitsaxena View Post

    I am not able to download the LineSize TechniSolve and *****
    Probably because they are supposed to be commercial and you need to pay for them.
    http://www.coolit.co.za/software.htm

  8. #8
    Join Date
    Mar 2009
    Location
    usa
    Age
    64
    Posts
    6
    Rep Power
    0

    Re: Calculating weight of refrigerant based on pipe size

    Thanks to everyone for your time and help. Please allow me to be more specific about my scenario. I am a plan and spec contractor in southern us where temps and humidity reach high 90s. Although we use manuf recom for pipe size based on length, lift, turns etc., there charts for adding refrigerant are often lacking specifics. My goal is to reduce or eliminate tech time spent adjusting charge. Some of our projects range from 50-150 split systems up to 20 tons. I could realize a significant increase in work efficiency if I could give my techs the tools they need to precisely weigh in the correct amount of 22/410. This would be especially helpful when completing projects in the winter. Already checking (still waiting) with Trane, Carrier and York. Thanks again for all your suggestions and help. I will eventually get around to researching each one.

  9. #9
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,266
    Rep Power
    46

    Re: Calculating weight of refrigerant based on pipe size

    Amount of refrigerant in the system has nothing to do with the lines size.

    Amount of refrigerant used should not exceed the volume of the receiver + a 1\4 of the condenser internal volume when refrigerant is pumped down.

  10. #10
    Join Date
    Mar 2009
    Location
    UKRAINE
    Age
    69
    Posts
    7
    Rep Power
    0

    Smile Re: Calculating weight of refrigerant based on pipe size

    Hi to all!!
    Quote Originally Posted by chemi-cool View Post
    Amount of refrigerant in the system has nothing to do with the lines size.
    Amount of refrigerant used should not exceed the volume of the receiver + a 1\4 of the condenser internal volume when refrigerant is pumped down.
    If you look in the textbook, then:
    Calculate the mass of the refrigerant gas is as follows:
    Mzapr = ρх.а * (0,4 * Visp + kg * Vres + Vzh.m), where
    ρх.а - the density of the refrigerant used; ρR22 = 1,3 kg/dm3, ρR404 = 1,04 kg/dm3;
    Visp - internal volume of air coolers;
    V res - the internal volume of the receiver cooling unit;
    V zh.m - internal volume of fluid lines;
    kg - factor Arrangement condenser:
    kg = 0,3 for the compressor-condenser units without a hydraulic pressure regulator condensation;
    kg = 0,4 using a hydraulic pressure regulator condensation (mounting the unit on the street or the
    Attached Images Attached Images

  11. #11
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,266
    Rep Power
    46

    Re: Calculating weight of refrigerant based on pipe size

    Very nice..........

    In real life, I dont believe it will work.

    There are too many other factors to consider but thats only my opinion.

  12. #12
    Join Date
    Mar 2009
    Location
    KZN, South Africa
    Age
    63
    Posts
    2,212
    Rep Power
    20

    Re: Calculating weight of refrigerant based on pipe size

    ^ Fair comment. How then, would one go about determining the correct system mass charge?

    Surely there would be some level of calculation first, followed by a charge adjustment - based on some criteria?

  13. #13
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,266
    Rep Power
    46

    Re: Calculating weight of refrigerant based on pipe size

    As I see it, it will be the receiver volume + about 1\3 of the condenser volume.

    Thats the amount when the refrigerant is pumped down.

    Why in the first place it is so important for you to calculate it?

    I have never seen a design for a refrigeration unit with the gas weight. Fill it and weight the amount, much more simple.

    Dry cooler unit will hold less refrigerant then a flooded one, long lines will influence it too, hot ambient will makes you use less, etc. etc...

  14. #14
    Join Date
    Mar 2009
    Location
    KZN, South Africa
    Age
    63
    Posts
    2,212
    Rep Power
    20

    Re: Calculating weight of refrigerant based on pipe size

    Quote Originally Posted by chemi-cool View Post
    Why in the first place it is so important for you to calculate it?
    Because I design heat-pumps for a living.

    The typical way we determine a gas fill has been to compute an initial charge & go in a little light. We then add charge progressively & test the system thoroughly. This can be a major time-consumer in the development stage.

    A more accurate method of determining the required charge would be wonderful.

  15. #15
    Join Date
    Mar 2009
    Location
    usa
    Age
    64
    Posts
    6
    Rep Power
    0

    Re: Calculating weight of refrigerant based on pipe size

    Quote Originally Posted by desA View Post
    Because I design heat-pumps for a living.

    The typical way we determine a gas fill has been to compute an initial charge & go in a little light. We then add charge progressively & test the system thoroughly. This can be a major time-consumer in the development stage.

    A more accurate method of determining the required charge would be wonderful.
    thank you desa, you are on the same line of thought I am. Saving time on jobs where the line length and rise varies over multiple systems and we must account for varying design perimeters. If some smart guy would figure it out so that contractors could use it, I would buy the software. It would defiantly save me labor.

  16. #16
    Join Date
    Mar 2009
    Location
    usa
    Age
    64
    Posts
    6
    Rep Power
    0

    Re: Calculating weight of refrigerant based on pipe size

    We are not talking about the same thing. Im talking airconditioning for people comfort. Sorry if I misslead you. Thanks.

  17. #17
    Join Date
    Mar 2009
    Location
    usa
    Age
    64
    Posts
    6
    Rep Power
    0

    Re: Calculating weight of refrigerant based on pipe size

    Thank you for your input. I believe after translating the units of measurement, it may be what I've been searching for. Thanks so much.

  18. #18
    Join Date
    Mar 2009
    Location
    KZN, South Africa
    Age
    63
    Posts
    2,212
    Rep Power
    20

    Re: Calculating weight of refrigerant based on pipe size

    ^ It is the same thing when you get down to it.

    As you would know, both heat-pumps & air-conditioning use the same cycle - we only worry about the hot end of the machine, aircon worries about the cold end...

    So, any methodology that would assist in the calculation of refrigerant charge would help the whole industry that relies on the vapour compression cycle.

  19. #19
    Join Date
    Mar 2009
    Location
    usa
    Age
    64
    Posts
    6
    Rep Power
    0

    Re: Calculating weight of refrigerant based on pipe size

    Quote Originally Posted by desA View Post
    ^ It is the same thing when you get down to it.

    As you would know, both heat-pumps & air-conditioning use the same cycle - we only worry about the hot end of the machine, aircon worries about the cold end...

    So, any methodology that would assist in the calculation of refrigerant charge would help the whole industry that relies on the vapour compression cycle.
    Yes, as employers who depend on finding productivity through ingenuity, this would or could be a milestone as it relates to cost saved and a job better done. Thanks.

  20. #20
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,175
    Blog Entries
    6
    Rep Power
    36

    Re: Calculating weight of refrigerant based on pipe size

    Since gas state of refrigerant is many,many,many... times greater volume of liquid one, any error in gas/liquid ratio calculation is many,many,many...... times amplified when we calculate refrigerant weight in system, and that is, I suppose, main reason why we still don't have any decently accurate method, formula or software for weight calculation.

  21. #21
    Join Date
    Mar 2009
    Location
    KZN, South Africa
    Age
    63
    Posts
    2,212
    Rep Power
    20

    Re: Calculating weight of refrigerant based on pipe size

    Ok, fair comment. That's a challenge for me then - I'll work on developing a suitable gas-charge estimation program. I have all the relevant gas/liquid/2-phase prediction data available - that's the easy part.

    The more difficult part would be to be able to estimate the relevant hold-up areas in the equipment - the pipes are a given.

    If anyone would like to contribute thoughts & ideas on this, I'll gradually develop an application. No promises, no pack-drill, but I think it would be useful.

  22. #22
    Join Date
    Mar 2009
    Location
    KZN, South Africa
    Age
    63
    Posts
    2,212
    Rep Power
    20

    Re: Calculating weight of refrigerant based on pipe size

    Some feedback
    I've been working on developing a first-principles refrigerant charge mass technique for an air-to-water heat pump system. It's actually not so easy.

    Using the rules, based on a system operating condition, the final mass turned out to be over-predicted.

    I'm now slowly bleeding the system off until the system begins to behave - & observing. The final runs will begin at low mass & then work upwards in steps of 100g.

    The AWHP is a rather testy device, it seems - especially near the top end of the temperature operating range. Slightly oversizing the TXV (one orifice #) can cause some very unstable hunting at the high pressures.

  23. #23
    garybb's Avatar
    garybb Guest

    Re: Calculating weight of refrigerant based on pipe size

    wher can i find an easy to read chart

  24. #24
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,192
    Rep Power
    60

    Re: Calculating weight of refrigerant based on pipe size

    Quote Originally Posted by garybb View Post
    wher can i find an easy to read chart
    I use Google, try this one..

    http://en.wikipedia.org/wiki/File:El...tbulb_type.svg
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  25. #25
    Join Date
    Oct 2004
    Location
    uk
    Age
    56
    Posts
    194
    Rep Power
    20

    Re: Calculating weight of refrigerant based on pipe size

    excellent Brian, simple and comprehensive as should be expected from one as experienced as yourself. i found it most helpful and shall use it as an example for all my engineers.
    thanks again. oh and bonne annee to you sir.

  26. #26
    Join Date
    Apr 2010
    Location
    Las Vegas, NV
    Age
    60
    Posts
    5
    Rep Power
    0

    Re: Calculating weight of refrigerant based on pipe size

    Quote Originally Posted by sheet59 View Post
    Thanks to everyone for your time and help. Please allow me to be more specific about my scenario. I am a plan and spec contractor in southern us where temps and humidity reach high 90s. Although we use manuf recom for pipe size based on length, lift, turns etc., there charts for adding refrigerant are often lacking specifics. My goal is to reduce or eliminate tech time spent adjusting charge. Some of our projects range from 50-150 split systems up to 20 tons. I could realize a significant increase in work efficiency if I could give my techs the tools they need to precisely weigh in the correct amount of 22/410. This would be especially helpful when completing projects in the winter. Already checking (still waiting) with Trane, Carrier and York. Thanks again for all your suggestions and help. I will eventually get around to researching each one.
    Been reading this thread. Very interesting and useful topic. This exact subject came up recently at work. A guy 'guesstimated' how much R22 a split system would need. Two trips to RSD later, he got it right.

    Here's a pdf from the crew at McQuay that google found for me. maybe it'll help.

    w w w. mcquay. com/ mcquaybiz/ literature/ lit_systems/ AppGuide/ AG_31-011_120407.pdf

    You'll have to delete the extra spacing in the url address, I'm too new to this site, it won't allow me to post a link yet.

    Dave

  27. #27
    Join Date
    Oct 2010
    Location
    Israel
    Posts
    5
    Rep Power
    0

    Re: Calculating weight of refrigerant based on pipe size

    Hi All,

    I have read your comments. However it seems I still don't understand how to calculate the total refrigerant mass i need in my system.

    If I have a system composed of Compressor, Condenser, Evaporator. How do I calculate the total refrigerant mass [kg] i need in my system?

    Thanks

Similar Threads

  1. Superheat and Subcooling
    By Chunk in forum Fundamentals
    Replies: 42
    Last Post: 15-01-2011, 02:24 AM
  2. Measurement of pipe lengths
    By batfink in forum Technical Discussions
    Replies: 11
    Last Post: 23-09-2008, 09:50 PM
  3. MHI FDCA400HKXRE4 Tech Info Please
    By L.JT in forum Trouble Shooting
    Replies: 5
    Last Post: 23-08-2008, 11:00 PM
  4. fun quiz
    By Brian23 in forum New to RE
    Replies: 6
    Last Post: 02-10-2007, 10:18 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •