    ups load



    Hi guys

    I need to find the heat output for a UPS battery pack, on the name plate it only states:
    3ph + N
    Input 44.6Amps
    Output 21.7Amps
    Can i assume that the difference in current is the the heat load when converted to watts ie: IxE =P

    Would appreciate your advice guys

    Thanks in advance

    Danny



  2. #2
    Join Date
    May 2006
    Location
    Sussex
    Posts
    364
    Rep Power
    20

    Re: ups load

    Best to get the manufacturer's name and google for that plus Btus/hr or Watts. Thing with UPS's is that they are normally on trickle load, ready to supply the full load of 21.7A in your case.

    As a similar: take a look at "APS SMART UPS 2200" (heat 275btu/hr), and some of their other units, in case that helps.

Similar Threads

  1. Sensible Heat Factor / capacity of Inverter split Systems at part load?
    By Greengrocer in forum Technical Speculations
    Replies: 31
    Last Post: 09-02-2009, 05:57 PM
  2. Heat transfer coefficient - Coolpack
    By Graham in forum Fundamentals
    Replies: 10
    Last Post: 28-05-2008, 01:08 AM
  3. Compressor loading, cooling, and range of operation.
    By Air duster in forum Fundamentals
    Replies: 10
    Last Post: 02-04-2008, 08:39 AM
  4. How is load divided between indoor units
    By mchild in forum Air Conditioning
    Replies: 26
    Last Post: 17-01-2008, 11:30 PM
  5. AKV versus higher load
    By Peter_1 in forum Industrial
    Replies: 20
    Last Post: 18-04-2004, 11:05 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •