    Oil separator

    There was some time ago a thread about oil separators on packs which I can't find back with the search engine.

    There seems to be problems with packs, working of R404a at low condensing pressure where the separator can't separate the oil.
    It's just like if you lower too much the discharge gas temperatures,that the separator isn't working properly anymore.

    A colleague of my had enormous troubles with it. As soon they increased HP, problem was gone. And as soon the decreased it again, problem came back.


    Ever heard of it?
    What is the technical explanation for this?
    What can be done to solve the problem so that can be worked with low high pressures without the oil problems?

  2. #2
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,248
    Rep Power
    46

    Re: Oil separator

    hi peter,

    at what pressure does the problem start?

    chemi

  3. #3
    Join Date
    Jun 2002
    Location
    UK
    Posts
    628
    Rep Power
    23

    Re: Oil separator

    Hi peter

    Yes ive had this on a few supermarket packs

    Best regards Mark

  4. #4
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,248
    Rep Power
    46

    Re: Oil separator

    hi mark


    and....... whats your verdict?


    chemi

  5. #5
    Join Date
    Jan 2003
    Location
    East Anglia
    Posts
    1,160
    Rep Power
    25

    Re: Oil separator

    Hi Peter,
    Like Mark, i have had it on some supermarket packs, Normally it has been down to the condenser fans coming in too early. Adjusting the cut in pressures has cured it.

    Hope this helps

    Regards

    Raymond

  6. #6
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,248
    Rep Power
    46

    Thumbs up Re: Oil separator

    hi guys,

    found something that explains why does it happend,
    http://www.temprite.com/downloads/te...randSludge.pdf

    at the bottom of page 2.

    chemi

Similar Threads

  1. Replies: 23
    Last Post: 06-06-2008, 02:27 PM
  2. Oil circulation, oil separator effect
    By aruiloba in forum Technical Speculations
    Replies: 19
    Last Post: 11-02-2006, 10:21 AM
  3. Diagrame Of Oil Separator
    By skags in forum Technical Discussions
    Replies: 9
    Last Post: 15-10-2005, 11:18 PM
  4. Oil line to compressors from temprite separator
    By Rob.S in forum Supermarket Refrigeration
    Replies: 7
    Last Post: 23-08-2005, 08:16 AM
  5. oil separator inefficient
    By jackcn in forum Technical Discussions
    Replies: 19
    Last Post: 26-12-2003, 03:07 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •