    Lightbulb Co2 Tank refrigeration system



    Hi guys.am new to this industry.and am being give a task of computing the required referigeration load for a Vertical Co2 polyeurethane(6" thik) insulated tank.The problem is when continoulsy running the chiller for 8-9 hrs, the pressure drop is negligeble..ie when the Chiller was switched on, the pressure was 21bar and after continously running for 9 hrs the pressure inside the tank was 20.5 bar..
    Should it be considered that the chiller used is inssufficient.Can somebody let me know how do i size the unit or the reasons that may be affecting the system
    It would be great if you could give me a few inputs..Following are the tank details:
    Tank capacity: 10000T
    6"thk polyeurethane insulated vertical tank.
    Ref: R404A



  2. #2
    Join Date
    Mar 2009
    Location
    India
    Age
    39
    Posts
    5
    Rep Power
    0

    Re: Co2 Tank refrigeration system

    sorry a small correction..capacity is 10 T and not 10000T..regret the mistake..

  3. #3
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    52
    Posts
    2,554
    Rep Power
    24

    Re: Co2 Tank refrigeration system

    Let me try to understand: you have a tank filled with 10 metric tons of liquid CO2 at 21bar (-18°C). Is that correct?
    What final temperature or pressure do you want to achieve? In how much time?

  4. #4
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,266
    Rep Power
    46

    Re: Co2 Tank refrigeration system

    CO2 liquid tanks come in 2 insulations: foamed polyurethane and vacuum.

    The evaporator is built inside the tank and has no fins, just bare pipes.

    Recently I had to find out the cooling capacity for a 10 ton vacuum insulated tank.
    It is 1KW at -20°C evaporating temp.
    If it is insulated with polyurethane, I assume it will be much more.
    The manufacturer should know that detail. contact him.

  5. #5
    Join Date
    Feb 2008
    Location
    manchester
    Posts
    80
    Rep Power
    17

    Re: Co2 Tank refrigeration system

    u need to get the evap down to -40degrees c. they are static coils and the ones i have installed for 10tons usually have a 2kw condensering unit on them 3phase. usually get a problem with 1phase comp electrics.

  6. #6
    Join Date
    Mar 2009
    Location
    India
    Age
    39
    Posts
    5
    Rep Power
    0

    Re: Co2 Tank refrigeration system

    Hi NoNickName, .Let me clear it.The Tank Max allowable working pressure is 24bar & hence the required operating pressure is around 18 bar..In order to maitain this pressure we have provided a chiller/ref unit.But inspite of operating this refer unit, the tank pressure is not comming down.Now would like to know what may the factors affecting it..?
    Thanks chemi cool...
    Hi KP3... Currently we have 4.5KW unit with 3 phase,440V,50Hz...

    Also as chemi cool mentioned about the evaporator coil built inside the tank, we did take this coil off from the tank & made modifications by allowing the CO2 gas to pass through the coil inside the chiller having referigerant. Is this clear or you would like to have an attachement indicating the same...

    Regds..Prashant

  7. #7
    Join Date
    Aug 2008
    Location
    ireland
    Age
    44
    Posts
    15
    Rep Power
    0

    Re: Co2 Tank refrigeration system

    I've worked on a few tanks over the past year and my understandingis that the condensing units are not meant to pulldown the pressure rather maintain a constant 19-18.5barg.

    As the liquid is used it will lower the temperature.

    try looking at other reasons

    too high pressure in the delivery lorry, normally the driver blows in down unless he's in a rush.

    back feed from another tank or process

    blow it down to 18bar and see if it maintains in over a few days.


    10ton tank is samll 1kw units grand

    hope it helps

  8. #8
    Join Date
    Mar 2009
    Location
    U.S.A.
    Posts
    320
    Rep Power
    20

    Re: Co2 Tank refrigeration system

    If this thing is brand new: Did they FIP the urethane?

    If its still curing out you will have a good excess heat load for some time to come!

Similar Threads

  1. Capillary Tube Characteristics
    By Chef in forum Fundamentals
    Replies: 9
    Last Post: 10-03-2009, 02:03 PM
  2. Refrigeration system simulation and optimization
    By autt in forum System Optimization
    Replies: 7
    Last Post: 05-12-2008, 03:59 PM
  3. Refrigeration system design
    By sachin9782 in forum Refrigerants
    Replies: 4
    Last Post: 19-11-2008, 08:27 PM
  4. Oil circulation system in Reciprocating refrigeration system
    By patilvasudeo in forum Fundamentals
    Replies: 5
    Last Post: 17-05-2008, 12:48 PM
  5. Refrigeration System for Agricultural Produce
    By Samarjit Sen in forum Fundamentals
    Replies: 13
    Last Post: 03-01-2008, 06:03 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •