    duct calcs



    we got given a spec for a duct addition to a landlords 250mm dia supply. The spec states the supply is
    5.0 l/s/m2 @ 30pa

    However we have to give the calc to show the additional will have on the pressure drop. Can anyone tell us what 8m of 250mm spirial duct + 4 90 elbows with a jet nozzle on the end works out at?
    We also have to install it to DW144 standards



  2. #2
    Join Date
    Nov 2005
    Location
    New Zealand
    Posts
    550
    Rep Power
    19

    Re: duct calcs

    Quote Originally Posted by multisync View Post
    we got given a spec for a duct addition to a landlords 250mm dia supply. The spec states the supply is
    5.0 l/s/m2 @ 30pa

    However we have to give the calc to show the additional will have on the pressure drop. Can anyone tell us what 8m of 250mm spirial duct + 4 90 elbows with a jet nozzle on the end works out at?
    We also have to install it to DW144 standards
    Hi Multi, You will find a duct calculator here

    http://www.fridgetech.com/calculators/

    Norm
    My wife used to say you never listen to a word I say at least I think that what she said

  3. #3
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: duct calcs

    Is the additional ductwork going to be on the Index circuit? If not then it probably won't add any additional static pressure.

  4. #4
    Join Date
    Jul 2008
    Location
    London
    Posts
    848
    Rep Power
    17

    Re: duct calcs

    Quote Originally Posted by frank View Post
    Is the additional ductwork going to be on the Index circuit? If not then it probably won't add any additional static pressure.

    Umm err what a err pardon?

  5. #5
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: duct calcs

    If you draw out a ductwork system on paper, the index circuit is the most tortuous route that the air has to travel, either input air or extract air, Ignoring all lesser branch ducts, the system resistance is calculated on this route.

    So, for instance, if you had a a 3 storey building with the fan on the roof extracting air from each floor, the fan would have to work harder to 'pull' the air from the ground floor than it would from the 3rd floor. In this case, the Index circuit would be the path to the ground floor, ignoring the branch to the 3rd floor grille.

    If the fan is capable of drawing air from the farthest/most difficult route, it can easily draw air from closer/lesser restrictive routes.

    Fluids will always take the path of least resistance, so if the grille nearest to the fan is wide open and the grille on the ground floor is partially closed, most of the fan volume will be drawn in from the nearest grille.

    The trick is to try and design a ductwork system where the most tortuous route has the least resistance, allowing you to select a smaller fan.

    Got to say though, not many people do this in reality.

  6. #6
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: duct calcs

    As an old commissioning engineer to possibly another old one, well described there Frank.

    Also the index is the terminal, air or water, that is fully open back to the fan/pump' no dampers or valves regulated on that route.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

Similar Threads

  1. Duct Size Calculations
    By hamidpia in forum Tools and Calculators
    Replies: 17
    Last Post: 21-06-2010, 01:56 PM
  2. Duct Sizing!
    By C_Henderson in forum Air Conditioning
    Replies: 3
    Last Post: 02-03-2008, 08:14 PM
  3. Daikin 7kW Cassette +supply duct to small office
    By Makeit go Right in forum Air Conditioning
    Replies: 6
    Last Post: 12-12-2007, 03:41 AM
  4. Duct Size Help!
    By Robearbam in forum Fundamentals
    Replies: 9
    Last Post: 04-04-2003, 01:44 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •