    matching indoor/outdoor units



    Hi,
    Should the indoor unit of a split ac should always be the same capacity as the outdoor unit ? I've read somewhere that indoor unit can be as much as 130% of the outdoor unit.
    Thanks in advance.



  2. #2
    Join Date
    Jul 2008
    Location
    London
    Posts
    848
    Rep Power
    17

    Re: matching indoor/outdoor units

    You are thinking of VRV for 130%

    Most would void warranty if you mixed and some would not run. Hitachi does have tha function but the dip switches must be adjusted to suit.

  3. #3
    Join Date
    May 2008
    Location
    saudi arabia
    Posts
    6
    Rep Power
    0

    Re: matching indoor/outdoor units

    I'm actually thinking of a standard split ac units not using vrv. What will be the effects of over sizing the indoor unit by 10-15 % higher than the condensing unit. Will the compressor burn in the long run?

  4. #4
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: matching indoor/outdoor units

    Quote Originally Posted by botching View Post
    I'm actually thinking of a standard split ac units not using vrv. What will be the effects of over sizing the indoor unit by 10-15 % higher than the condensing unit. Will the compressor burn in the long run?
    Why would you oversize indoor unit when they are sold in matched pairs?

  5. #5
    Join Date
    Jun 2008
    Location
    India
    Age
    56
    Posts
    64
    Rep Power
    16

    Re: matching indoor/outdoor units

    Quote Originally Posted by botching View Post
    What will be the effects of over sizing the indoor unit by 10-15 % higher than the condensing unit. Will the compressor burn in the long run?
    The Ac manufacturers match the Indoor and outdoor units to have the right system balancing, to deliver required cooling capacity without exceeding compressor safe operating parameters. Unless you have a manufacturer giving you options of different Indoor units, it may not be worth your time in the field. POssibility of compressor burning will depend on the suction gas temperature for motor cooling and the operating pressure ratio. If the units are incorrectly matched against the mfr. specs., you can expect it to nuisance trip when you need it the most i.e. peak summer.

  6. #6
    Join Date
    May 2008
    Location
    saudi arabia
    Posts
    6
    Rep Power
    0

    Re: matching indoor/outdoor units

    i'm actually in the process of selecting several combination of trane indoor/outdoor units (dx coils,5-20 tr) where the AHU (fresh air handling units) will be matched with trane voyager series condensing units. I'm getting 10.3 tons total capacity for one AHU while the corresponding condensing units capacity is 10 tr max. I think with little oversizing(indoor units), there won't be a big reduction in the performance of the units.

  7. #7
    Join Date
    Dec 2001
    Location
    UK
    Posts
    137
    Rep Power
    23

    Re: matching indoor/outdoor units

    The manufacturers make their matches to do a specific job without the evaporating and condensing pressures going outside of useable limits or the need for expensive controls.
    If you take a large evaporator and match it with a smaller sized condensing unit the evaporating temperature will go up resulting in high sensible cooling.
    if the system is a heatpump though the condensing temperature in heating will be too low due to the large coil in the ahu.
    if you fit a smaller evaporator to a larger condensing unit the evaporating temperature will fall in cooling and the condensing temperature will rise in heating.
    The manufacturers are limited by the compressor which usually is designed for -10°C to +10°C saturated suction and a 35° to 55°C condnsing temperature as well as a need for the coils to not get too hot or more important not get too cold and freeze.
    A VRV/VRF has the capability due to its fancy controls and outdoor unit design to limit the outputs off the indoor units whilest maximise the outputs on the outdoor coils.
    What you need to do is find a condensing unit that will provide the required duty with a saturated suction temp of around 2°C for comfort cooling or 7°C for high sensible cooling iat the design temperature BUT doesn't go above 10°C saturated suction temp at the MAXIMUM ambient likely to be seen.

    Brit

Similar Threads

  1. Matching Compressor with the coil.
    By Savannah Tom in forum Air Conditioning
    Replies: 1
    Last Post: 06-09-2007, 02:37 PM
  2. Matching Evaporator with Condensing Unit
    By Abe in forum Technical Discussions
    Replies: 12
    Last Post: 25-07-2001, 08:57 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •