    fujitsu fault codes



    Hello guys, could any of you tell me what fault code E,01 is on a fujitsu cassette. Mod number AUY30RLB-W On R22. Machine spins indoor fan and very little else, all connections and wiring ok, fuses on indoor and outdoor boards ok.

    Andy



  2. #2
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: fujitsu fault codes

    Communication error indoor-outdoor. Check wiring and check voltage between terminal 1 and 2(N) with analogue multimeter for voltage swings.

  3. #3
    Join Date
    May 2006
    Location
    Isle of Wight, Uk
    Age
    47
    Posts
    424
    Rep Power
    20

    Re: fujitsu fault codes

    Unfortunately, no longer have an analogue meter but the volatge measured with me digital one was anywhere between 50-70 volts.

  4. #4
    Join Date
    Jul 2007
    Location
    Australia
    Age
    50
    Posts
    1,845
    Rep Power
    20

    Re: fujitsu fault codes

    It should be about 70-100v as each unit puts out 20-60V out of phase to the other.

    Cut power, disconnect one of the comms cables at either indoor or outdoor terminal. Switch power back on and see which one is good and reading 20-60V and which one is not putting out 20-60V.

    edit: It's best to repeat this at both the indoor and the outdoor units to rule out a problem with the interconnecting cable itself.
    Last edited by paul_h; 06-03-2009 at 01:49 AM.

  5. #5
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: fujitsu fault codes

    You only disconnect wire from indoor-to-outdoor connection cable at terminal 1 at one connector (either indoor unit or outdoor unit) and measure voltage at terminal (1 and 2) at both indoor and outdoor connectors with that wire disconnected.
    One that doesn't produce that voltage swings has faulty PCB.
    Best is to measure voltage shortly after unit power up!

  6. #6
    Join Date
    Jul 2007
    Location
    Australia
    Age
    50
    Posts
    1,845
    Rep Power
    20

    Re: fujitsu fault codes

    Quote Originally Posted by nike123 View Post
    You only disconnect wire from indoor-to-outdoor connection cable at terminal 1 at one connector (either indoor unit or outdoor unit) and measure voltage at terminal (1 and 2) at both indoor and outdoor connectors with that wire disconnected.
    One that doesn't produce that voltage swings has faulty PCB.
    Best is to measure voltage shortly after unit power up!
    Lets say you are at the outdoor unit and have disconnected the comms line there and test.
    If you find the outdoor unit being low volatge or not fluctuating, but the interconnecting cable showing 20-50V, it's fair to condemn the outdoor PCB as there's no cabling between you and the outdoor.
    But if the outdoor was 20-50V but the cable from the indoor was 0V, would you just condemn the indoor PCB?

    My point was, in that case, repeat the check at the indoor unit, as it could be a bad interconnecting cable that is the cause of reading 0V at the outdoor from the indoor unit line. The indoor unit could be fine.

    So in some cases, you only need to do one check, that's the test that has the unit you are testing at show faulty.
    In other cases you need to test twice, that's when the cable is testing dead and you have to remove the interconnecting cable as a possible source of fault.

    Edit: Here , it's terminal 3 that is the comms line, not terminal 1, terminal 1 is active here.
    I don't know what it is in the UK, but check before you disconnect in case terminal 1 is the active.
    Last edited by paul_h; 06-03-2009 at 10:32 AM.

  7. #7
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: fujitsu fault codes

    That is why I wrote first to test interconnecting cable and than voltage. But your way is equally good, and I did not read it thoroughly at first, and since English is not my native, some details are not seen that time.

    Sorry, it was not my intention to dispute your answer, it is only intended to clarify some small things since I thought (at that time) that is not clear.


  8. #8
    Join Date
    Jul 2007
    Location
    Australia
    Age
    50
    Posts
    1,845
    Rep Power
    20

    Re: fujitsu fault codes

    No problems, easier just to double check the comms when diagnosing rather than using some other way of testing the cable.

    Yes, your units seem different if terminal 1 is the comms line. Something for both of us to bear in mind when telling people from other countries what terminals to check! Same actual terminal we are testing, but your's are numbered right to left, but ours are numbered left to right.
    Attached Images Attached Images
    Last edited by paul_h; 06-03-2009 at 01:08 PM.

  9. #9
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: fujitsu fault codes

    Quote Originally Posted by paul_h View Post
    No problems, easier just to double check the comms when diagnosing rather than using some other way of testing the cable.

    Yes, your units seem different if terminal 1 is the comms line. Something for both of us to bear in mind when telling people from other countries what terminals to check! Same actual terminal we are testing, but your's are numbered right to left, but ours are numbered left to right.

    Not always, sometimes!

Similar Threads

  1. Daikin fault codes
    By Markie in forum Air Conditioning
    Replies: 16
    Last Post: 13-01-2009, 01:58 AM
  2. standardisation of fault codes?
    By kelvin kline in forum Air Conditioning
    Replies: 1
    Last Post: 10-10-2007, 12:30 AM
  3. MHI, Sanyo & Fuijitsu Complete Fault Codes
    By aeb200 in forum Air Conditioning
    Replies: 1
    Last Post: 16-11-2005, 01:11 PM
  4. Fujitsu AOT24PMAL Fault Codes
    By johnmart in forum Trouble Shooting
    Replies: 5
    Last Post: 19-04-2004, 06:39 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •