Correct Evaporator TD Calculation
Hello everyone. In commercial refrigeration (walk-in freezers/coolers), we typically estimate the evaporator TD by dividing condensing unit capacity by evaporator capacity (x10)...
But I would like to know the most accurate way to calculate this TD. Or if not calculation, must I find the saturated suction temp at which evaporator capacity is closest to condensing unit capacity (and then TD is room temp - that SST)?
Thanks in advance for your insights.
-
03-03-2009, 05:53 PM #2
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,151
- Blog Entries
- 6
- Rep Power
- 36
Re: Correct Evaporator TD Calculation
What is purpose of that estimation?
-
03-03-2009, 08:20 PM #3
Re: Correct Evaporator TD Calculation
Hi nike123. The purpose is to make sure the condensing unit to evaporator capacities are within acceptable range, to ensure correct humidity in the room. So for a storage freezer, a TD of 11 may be fine, but for a flower cooler, a TD of 8 or 9 would be more appropriate. Thanks in advance.
-
03-03-2009, 08:32 PM #4
Re: Correct Evaporator TD Calculation
PS: Those examples were in deg F... So the freezer TD was 6.1 deg K and the flower cooler was 4.4-5 deg K.
Similar Threads
-
Flash gas calculation software
By nike123 in forum Tools and CalculatorsReplies: 4Last Post: 12-03-2009, 09:25 AM -
Calculation bypass buffer tank volume
By abbasi in forum New TechnologiesReplies: 3Last Post: 16-10-2008, 06:19 AM -
NH3 thermosiphon evaporator calculation
By cygbob in forum NH3Replies: 3Last Post: 27-11-2007, 10:00 AM -
how can i correct the dilution of the oil lubricant when i use hydrocarbons?
By mebluna in forum RefrigerantsReplies: 5Last Post: 11-07-2007, 03:06 AM -
Cooling load calculation
By raviperumal in forum Technical DiscussionsReplies: 6Last Post: 02-03-2007, 04:09 AM