    Less refrigerant used



    Here is claim:

    10.1.1 Specific features
    (1) Less refrigerant charge amount due to use of double phase refrigerant flow system. The total refrigerant charge amount has been
    reduced by more than 50%.
    That is MHI Comercial series Heat pump non-inverter air-conditioner ceiling recessed type single split system
    And here is refrigerant diagram:



    Could someone explain how this works and what is function of these marked parts in this refrigeration circle in both heating and cooling mode, since I found it difficult to understand?

    And this is another variance:

    Last edited by nike123; 02-03-2009 at 09:41 AM.



  2. #2
    Join Date
    Aug 2007
    Location
    Russia
    Posts
    138
    Rep Power
    21

    Re: Less refrigerant used

    I guess in cooling mode part2 is for oil return from accumulator.
    Part 1 is for "flash gas+ liquid" injection in suction line if discharge temp. (thermistor Th-d) becomes too high.
    Part 3 is to increase sub cooling. In this case after the capillary tube we have less capacity decrease.
    Part 4 is used in heating mode to prevent outdoor heat exchanger frosting (thermistor Tho-R)
    P.S. All above is IMHO

  3. #3
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,175
    Blog Entries
    6
    Rep Power
    36

    Re: Less refrigerant used

    Quote Originally Posted by narkom View Post
    I guess in cooling mode part2 is for oil return from accumulator.
    Part 1 is for "flash gas+ liquid" injection in suction line if discharge temp. (thermistor Th-d) becomes too high.
    Part 3 is to increase sub cooling. In this case after the capillary tube we have less capacity decrease.
    Part 4 is used in heating mode to prevent outdoor heat exchanger frosting (thermistor Tho-R)
    P.S. All above is IMHO

    Ok, thanks. That seams explain function of parts, but I am eager to know how is achieved that 50% less refrigerant in system.

  4. #4
    Join Date
    Aug 2007
    Location
    Russia
    Posts
    138
    Rep Power
    21

    Re: Less refrigerant used

    Is it really like this? Have you compared the refrigerant charge with Daikin or ME units charge for the same capacity?
    Last edited by narkom; 03-03-2009 at 05:33 PM.

  5. #5
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,175
    Blog Entries
    6
    Rep Power
    36

    Re: Less refrigerant used

    Quote Originally Posted by narkom View Post
    Is it really like this? Have you compared the refrigerant charge with Daikin or ME units charge for the same capacity?
    1,1 kg of R22 for heat pump of 5,7kW cooling capacity.

    Bare in mind that this is model from 2000 year or earlier.
    Same size and year Fujitsu 1,7kg of R22.

  6. #6
    Join Date
    Aug 2007
    Location
    Russia
    Posts
    138
    Rep Power
    21

    Re: Less refrigerant used

    ME charges 2.2 kg for heat pump of 5.4kW.
    I guess MHI with 1.1 kg has minimum sub cooling in condenser. Note that they give only 20m height difference for 208 and 258 units.
    ME gives 40m.
    So no miracle at all))

  7. #7
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,175
    Blog Entries
    6
    Rep Power
    36

    Re: Less refrigerant used

    Quote Originally Posted by narkom View Post
    ME charges 2.2 kg for heat pump of 5.4kW.
    I guess MHI with 1.1 kg has minimum sub cooling in condenser. Note that they give only 20m height difference for 208 and 258 units.
    ME gives 40m.
    So no miracle at all))
    You don't telling me that ME comes already charged for 40m?

  8. #8
    Join Date
    Aug 2007
    Location
    Russia
    Posts
    138
    Rep Power
    21

    Re: Less refrigerant used

    ME has a large suction accumulator and comes already charged for 30 m.
    MHI is charged for 5 m.
    Concerning "double phase refrigerant flow'
    I read that the
    condensed high pressure refrigerant is reduced in pressure by the capillary tubes in the outdoor unit. This results in a “two-
    phase refrigerant” of reduced pressure in the liquid section of the piping. The density of this two-phase refrigerant is 1/3~
    1/2 of that of the high pressure liquid refrigerant, and thus is required in smaller amounts . As a result,
    the length of the piping can be extended further, and the effects of height differences are reduced.

  9. #9
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,175
    Blog Entries
    6
    Rep Power
    36

    Re: Less refrigerant used

    Quote Originally Posted by narkom View Post
    ME has a large suction accumulator and comes already charged for 30 m.
    MHI is charged for 5 m.
    Concerning "double phase refrigerant flow'
    I read that the
    condensed high pressure refrigerant is reduced in pressure by the capillary tubes in the outdoor unit. This results in a “two-
    phase refrigerant” of reduced pressure in the liquid section of the piping. The density of this two-phase refrigerant is 1/3~
    1/2 of that of the high pressure liquid refrigerant, and thus is required in smaller amounts . As a result,
    the length of the piping can be extended further, and the effects of height differences are reduced.
    From what i see in these diagrams that is different only in heating mode, in comparison with regular units, since in cooling mode, regular units also have two phase flow.

    Do you have ME refrigerant diagram of simmilar unit for comparison?

  10. #10
    Join Date
    Aug 2007
    Location
    Russia
    Posts
    138
    Rep Power
    21

    Re: Less refrigerant used

    Quote Originally Posted by nike123 View Post
    Do you have ME refrigerant diagram of simmilar unit for comparison?
    http://www.mrslim.com/UploadedFiles/...C%20PUH-EK.pdf
    The same circulation system.

  11. #11
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,175
    Blog Entries
    6
    Rep Power
    36

    Re: Less refrigerant used

    Quote Originally Posted by narkom View Post
    Thanks Narkom! It is same principle.

    Here I see bypass valve. What is its purpose here?

Similar Threads

  1. Superheat and Subcooling
    By Chunk in forum Fundamentals
    Replies: 42
    Last Post: 15-01-2011, 02:24 AM
  2. Leak Testing?
    By Thana in forum Trouble Shooting
    Replies: 36
    Last Post: 31-08-2010, 02:57 PM
  3. CARE refigerants by BOC
    By dogma in forum Refrigerants
    Replies: 8
    Last Post: 23-03-2010, 01:39 PM
  4. MHI FDCA400HKXRE4 Tech Info Please
    By L.JT in forum Trouble Shooting
    Replies: 5
    Last Post: 23-08-2008, 11:00 PM
  5. fun quiz
    By Brian23 in forum New to RE
    Replies: 6
    Last Post: 02-10-2007, 10:18 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •