    Hello, guys!

    Do you know what velocity in water header is suitable?

    I'm talking about the water header of Air-Cooling and Dehumidifying Coils.

    From ASHRAE, we know the water velocity inside the tube is about 0.3-2.4m/s, but ASHRAE doesn't tell us about the velocity range of the water header. What's you opion?

    Thank you!



  2. #2
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Water velocity in water header

    I wont go into all the variations to this answer but will point you towards this e-book.

    http://www.haestad.com/library/books...tml/wwhelp.htm

    Click on the index and then the letter "V" for velocity, select What is Maximum.....
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  3. #3
    Join Date
    Dec 2008
    Location
    China
    Posts
    87
    Rep Power
    16

    Re: Water velocity in water header

    This book is gorgeous!Thank you very much, Brian! I find my answer.

    It's a pity that I can't download this book.

  4. #4
    Join Date
    Nov 2010
    Location
    Germany
    Age
    39
    Posts
    120
    Rep Power
    14

    Re: Water velocity in water header

    Generally, the water velocity in header should be 0.2-0.3m/s. But,i use this kind of sizing only for main header. For instance, if you use the underfloor cooling with the manifolds, than it depends of the valves on it..For what do you need it exactly? Be careful regarding this stuff, it is just a piece of pipe but it has a great influence on the system..

Similar Threads

  1. Water velocity in Shell and tube HE
    By wilsoncheung in forum Industrial
    Replies: 15
    Last Post: 07-04-2009, 07:59 PM
  2. Fact or Fiction
    By david.findlay in forum Fundamentals
    Replies: 40
    Last Post: 09-03-2009, 06:19 PM
  3. pure water from air
    By Lc_shi in forum New Technologies
    Replies: 32
    Last Post: 26-02-2009, 12:25 PM
  4. what is suitable water flow velocity in Evaporator?
    By chistine in forum Commercial
    Replies: 7
    Last Post: 11-09-2006, 05:26 PM
  5. Building a wine cabinet
    By Rory in forum Technical Discussions
    Replies: 38
    Last Post: 13-07-2004, 08:28 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •