03-03-2009, 08:46 PM #1
Re: need some answers plaease
ok went back to site today.after speaking to the technical bloke in the suppliers heres what i did.
1. fit new filter drier
2.fit new valve and orifice no:3
also spoke to the original engineer who wasnt sure if he charged unit with134a or 407c-as supplied and confirmed with technical bloke at the suppliers-who got a bit grumpy i think
ran unit and here is what i got
unit:beermaster bmo150-1
refrigerant:r407c
room temp at time:+17 celcius-evap display
suction:4.4 barg/62 psi
discharge:14 barg/200 psi
suction line temp by expansion bulb:+12 celcius
liquid line @expansion valve:+23 celcius
liquid line into condenser:+56 celcius
liquid line leaving condenser:+31celcius
air on evap:+18 celcius
air off: +12 celcuis
cond air on:+18 celcuis-my thermometer
air off:+29 celcuis
i work this as givin me a superheat of 6 celcius and it seems to pull temp -at15 when left .no condensation on compressor.going to return on thursday and see how it running.what do all of you think of the above?i know it a bit long but thanks again.
-