    need some answers plaease



    hi all hope some of you can help.
    i have a beer master unit that wont pull temp below 16celcius. the suction pressure is 2.5 barg running on r134
    the unit has condensation on the compressor covering about 80% of it-only the top has'nt. also the liquid line is warm to touch right up until the expansion valve - is this normal? is it possible the expansion valve is stuck open? if so how would i check
    thanks in advance



  2. #2
    Join Date
    Jul 2005
    Location
    luton
    Age
    42
    Posts
    87
    Rep Power
    19

    Re: need some answers plaease

    sorry forgot to add the condensing unit was changed 4 months ago because of the same problems

  3. #3
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: need some answers plaease

    and the other readings to help in our diagnosis are ??
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  4. #4
    Join Date
    Jan 2007
    Location
    scotland
    Age
    46
    Posts
    159
    Rep Power
    18

    Re: need some answers plaease

    what type of expansion valve is fitted to this unit if its a danfoss tev it has a screw in adjustment.by turning it in clockwise would close the valve and anti the oppisite.
    does sound like the valve is flooding back to your comp but could be incorrect sizing of orifice or under sized unit.Is this a case or a coldroom and did the problem start straight after the new unit was fitted or a while later and has any other works been done on this system.

  5. #5
    Join Date
    Jul 2005
    Location
    luton
    Age
    42
    Posts
    87
    Rep Power
    19

    Re: need some answers plaease

    sorry i know there not alot of info. goin back to site monday just wondered what your thoughts would be.what other info would u need and is it possible the expansion valve can do this?

  6. #6
    Join Date
    Jul 2005
    Location
    luton
    Age
    42
    Posts
    87
    Rep Power
    19

    Re: need some answers plaease

    it is a danfoss valve.a tex2 i think or a tx2 with a number 4 orifice the problem has been there for nearly a year. another engineer worked on the unit and determined that it was the condensing unit at fault and changed it 4 months ago. my problem is that every 2-3 months we get a callback for the same problem/same symtoms. i have just recently got involved although i did tell them at the time i was"nt sure it was the condensing unit from what i was told.customer says unit ran ok when unit was changed until recently and no other work was done on it since that till now.is it possible te valve stuck open ? if so how would you check?
    thanks in advance any help much appreciated
    Last edited by sean1; 28-02-2009 at 11:46 PM.

  7. #7
    Join Date
    Jul 2005
    Location
    luton
    Age
    42
    Posts
    87
    Rep Power
    19

    Re: need some answers plaease

    sorry i know it alot of questions. but what can cause the compressor to have condensation build up on it? is it normal for the liquid line to be still warm just before the expansion valve? just seeking more knowledge and experience

  8. #8
    Join Date
    Jan 2007
    Location
    scotland
    Age
    46
    Posts
    159
    Rep Power
    18

    Re: need some answers plaease

    first thing is to make sure condensor is clean but being 4 months old wouldnt expect it to be dirty much,second if it has a sight glass on the liquid line is it bubbling or clear and does it have a moisture indicator fitted.if showing moisture in systm change drier and fit a new valve+orifice but try and find out if its the correct rating as a tex is for r22 not r134a and a size four is quite big but as i dont know the size of the load it might be correct.hope this is some help

  9. #9
    Join Date
    Jul 2005
    Location
    luton
    Age
    42
    Posts
    87
    Rep Power
    19

    Re: need some answers plaease

    fowlie thanks for the reply. yes condenser is clean and fans working fine[as you said not that old]sight glass is fitted[as standard i think]it is clear but it a light purple coluor which says caution on the outside of the glass. i planned on vaccing and re-charging unit on monday. do u think i should also change expansion valve and drier? brian ur input would be much appreciated-would i be better gettin more temps/pressures before going forward?
    sorry fowlie just re-read your message will check valve size etc monday when on site climate centre only 5 min up road hopefully get sorted in one day!
    Last edited by sean1; 01-03-2009 at 12:22 AM.

  10. #10
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: need some answers plaease

    Was the old condensing unit operating on R134a?

    What gas is the TEV rated for?

  11. #11
    Join Date
    Dec 2004
    Location
    Australia
    Age
    52
    Posts
    519
    Rep Power
    20

    Re: need some answers plaease

    Quote Originally Posted by sean1 View Post
    it is a danfoss valve.a tex2 i think or a tx2 with a number 4 orifice
    What's a beer master unit?

    No 4 orifice is pretty big for commercial sounds like it may be too big. (depends on application)

  12. #12
    Join Date
    Dec 2007
    Location
    lebanon
    Posts
    130
    Rep Power
    17

    Re: need some answers plaease

    hi
    i think there is a problem in the expansion valve orifice .it seem that it feeds too much refrigerant to the evaporator.orifice must match the capacity of cndensing unit @the desired evaporation temp.ther is some thing wrong here txv for 134 is tn or ten not tx so check it

  13. #13
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: need some answers plaease

    Quote Originally Posted by Temprite View Post
    What's a beer master unit?

    No 4 orifice is pretty big for commercial sounds like it may be too big. (depends on application)
    Temprite, I was thinking the same.
    What's the type and brand of the condensing unit?
    Wrong gas as Frank suggested is of course also possible.
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  14. #14
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: need some answers plaease

    We discussed Beermaster coolers here

    http://www.refrigeration-engineer.co...ad.php?t=10788

  15. #15
    Join Date
    Jul 2005
    Location
    luton
    Age
    42
    Posts
    87
    Rep Power
    19

    Smile Re: need some answers plaease

    ok went back to site today.after speaking to the technical bloke in the suppliers heres what i did.
    1. fit new filter drier
    2.fit new valve and orifice no:3

    also spoke to the original engineer who wasnt sure if he charged unit with134a or 407c-as supplied and confirmed with technical bloke at the suppliers-who got a bit grumpy i think
    ran unit and here is what i got

    unit:beermaster bmo150-1
    refrigerant:r407c
    room temp at time:+17 celcius-evap display
    suction:4.4 barg/62 psi
    discharge:14 barg/200 psi
    suction line temp by expansion bulb:+12 celcius
    liquid line @expansion valve:+23 celcius
    liquid line into condenser:+56 celcius
    liquid line leaving condenser:+31celcius
    air on evap:+18 celcius
    air off: +12 celcuis
    cond air on:+18 celcuis-my thermometer
    air off:+29 celcuis
    i work this as givin me a superheat of 6 celcius and it seems to pull temp -at15 when left .no condensation on compressor.going to return on thursday and see how it running.what do all of you think of the above?i know it a bit long but thanks again.

  16. #16
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: need some answers plaease

    It appears to need a little more refrigerant. Is the sight glass clear?

  17. #17
    Join Date
    Jul 2005
    Location
    luton
    Age
    42
    Posts
    87
    Rep Power
    19

    Re: need some answers plaease

    yes but was getting dark when i left site will check again on thursday.but how did you come to that conclusion?- just curious does all else seem ok.are these typical ie should this be what i should be expecting and checking-roughly
    Last edited by sean1; 03-03-2009 at 09:57 PM.

  18. #18
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: need some answers plaease

    Quote Originally Posted by sean1 View Post
    liquid line @expansion valve:+23 celcius

    liquid line leaving condenser:+31celcius

    You still have big drop of liquid line temperature (8K) from condenser to TXV.
    Describe what is at that line and its length (together with elbows valves etc...) and insulation and temperatures at pipe location.
    Last edited by nike123; 04-03-2009 at 03:07 PM.

  19. #19
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: need some answers plaease

    I'm thinking that liquid line temp was actually taken at the drip leg. It should have been measured at the outlet of the receiver.

  20. #20
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: need some answers plaease

    Quote Originally Posted by Gary View Post
    I'm thinking that liquid line temp was actually taken at the drip leg. It should have been measured at the outlet of the receiver.
    What is drip leg?

  21. #21
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: need some answers plaease

    Quote Originally Posted by nike123 View Post
    What is drip leg?
    The drip leg is the pipe between the condenser outlet and the receiver inlet.

    If the sight glass is clear, then the subcooling at the receiver outlet is probably pretty close to the subcooling at the TXV inlet... and the refrigerant charge is probably sufficient.

  22. #22
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: need some answers plaease

    Quote Originally Posted by Gary View Post
    The drip leg is the pipe between the condenser outlet and the receiver inlet.

    If the sight glass is clear, then the subcooling at the receiver outlet is probably pretty close to the subcooling at the TXV inlet... and the refrigerant charge is probably sufficient.
    Ok, but what would be cause of cca 8K temperature drop from condenser outlet to receiver inlet.

  23. #23
    Join Date
    Jul 2005
    Location
    luton
    Age
    42
    Posts
    87
    Rep Power
    19

    Re: need some answers plaease

    reading was taken between condenser outlet and receiver
    Last edited by sean1; 04-03-2009 at 08:48 PM.

  24. #24
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: need some answers plaease

    Quote Originally Posted by sean1 View Post
    reading was taken between condenser outlet and receiver
    The reading should be taken in the liquid line after the receiver... which is probably where the sight glass is.

    On systems which have no receiver, the bottom of the condenser serves that function... so on such a system we would take the reading at the outlet of the condenser.
    Last edited by Gary; 04-03-2009 at 09:11 PM.

  25. #25
    Join Date
    Jul 2005
    Location
    luton
    Age
    42
    Posts
    87
    Rep Power
    19

    Re: need some answers plaease

    thanks gary will check tommorrow

  26. #26
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: need some answers plaease

    Quote Originally Posted by nike123 View Post
    Ok, but what would be cause of cca 8K temperature drop from condenser outlet to receiver inlet.
    There can be some condensing going on in the drip line, especially at the condenser end... so we can't trust that measurement. Also, we don't know if the TXV end of the liquid line is in the refrigerated space or not. If it is, it's temp could be considerably lower.

    So... we don't really know if that 8K difference exists.

    And the fact that the sight glass is clear indicates that it has sufficient subcooling at that point, which means the temp at the receiver outlet/sight glass must be pretty close to the temp at the TXV.
    Last edited by Gary; 04-03-2009 at 09:26 PM.

  27. #27
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: need some answers plaease

    Quote Originally Posted by Gary View Post
    There can be some condensing going on in the drip line, especially at the condenser end... so we can't trust that measurement.
    Ok, thanks for clarification.
    When you say that is some condensing going on in drip line, what is cause of that condensation except of ambient temperature (if any other)?

  28. #28
    Join Date
    Jul 2005
    Location
    luton
    Age
    42
    Posts
    87
    Rep Power
    19

    Re: need some answers plaease

    txv is in refrigerated space. will check all u ave said and post results.once again thanks to everyone

Similar Threads

  1. air conditioning questions and answers
    By sid in forum Tools and Calculators
    Replies: 7
    Last Post: 20-08-2007, 01:06 AM
  2. apprentice requesting answers
    By napoleon in forum Technical Discussions
    Replies: 16
    Last Post: 25-01-2006, 08:37 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •