    Bad heat pump design (TXV)?



    The heat pumps i´ve been having issues with recently I´m sure are down to design issues.

    I have noticed something which I think is quite relevent to the opertaion of the heat pump.

    1. The TXV bulb is on the bottom (horizontal) of a "u" bend.

    2. The The TXV bulb is after the equalising line for the TXV.

    3. Both the bulb and equalising line are after the 3-way valve.

    I believe all these things are incorrect and would lead to the problems I have been having with the suction line pressures and temperatures flucuating. Am I correct in thinking this?

    I have attached pictures to demonstrate what I mean. The suction line bends up behind the the accumulator then bends 180º on to the top of the accumulator.

    I´ve made a new thread so not to confuse my other thread. If the mods want me to put this in there, then let me know and i´ll post it in there instead.








  2. #2
    Join Date
    Aug 2008
    Location
    ENGLAND
    Age
    54
    Posts
    27
    Rep Power
    0

    Re: Bad heat pump design (TXV)?

    Looks like an Alto to me. Reverse engineering at its best ha. The bulb should be as close to the evap as possible after any distribution pipes from the evap, prefferably on a level pipe and before the external equalisation line and it should be lagged to prevent it being affected by airflows through the machine. As for the external equalisation, it looks like it is in the wrong place to me.

    Hope this helps.

  3. #3
    Join Date
    Mar 2005
    Location
    Lanzarote
    Age
    41
    Posts
    372
    Rep Power
    20

    Re: Bad heat pump design (TXV)?

    Exactly what I though, thanks. Yes it is an Alto, well spotted.

  4. #4
    Join Date
    Aug 2006
    Location
    China
    Age
    55
    Posts
    52
    Rep Power
    18

    Re: Bad heat pump design (TXV)?

    yes, what you think is very correct.
    TXV is a very important part in refrigeration system, there is strict demands about its installation: TXV must be vertical
    the bulb and equalizing tube must installed on horizontal pipe.
    equalizing tube must be downstream of the bulb

  5. #5
    adchesney's Avatar
    adchesney Guest

    Re: Bad heat pump design (TXV)?

    I have an Alto HY40 and am looking after an engineers manual to help solve a constant "E4" error/fault.

    Also, thank you for the Mods suggestions

    regards

    Andrew at Chesney dot org

Similar Threads

  1. Design heat pump for a pool
    By rolandh in forum Heat Pumps
    Replies: 10
    Last Post: 23-09-2010, 10:50 AM
  2. Heat Pump Design
    By behmin in forum Heat Pumps
    Replies: 10
    Last Post: 22-03-2009, 09:00 PM
  3. Air to water split heat pump design
    By ginger jiang in forum Heat Pumps
    Replies: 3
    Last Post: 26-02-2009, 08:00 AM
  4. frostles heat pump
    By Lc_shi in forum New Technologies
    Replies: 27
    Last Post: 31-03-2008, 07:53 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •