What will cause eva pressure fluctuate?
I have a question to discuss and hope you will be interested.
Its a air-cooled cooling air unit, thermal expansion valve with distributor. Air come out of evap is about 10 degree. Now the problem is the evaporating pressure fluctuates about 50 kPa, I wanna know what cause the fluctuation.
Any possible answer provided is welcome!
-
27-02-2009, 01:02 PM #2
Re: What will cause eva pressure fluctuate?
Lots of things could cause that. Stab in the dark but how does the unit control head pressure, if the condenser fan cuts in and out on a pressure switch that could cause it or maybe the thermostaic expansion valve is hunting.
need lots more info to help, how frequent is the fluctuation, air on air off running conditions gas type and running pressures, delta T etc.
-
27-02-2009, 01:22 PM #3
Re: What will cause eva pressure fluctuate?
Probably caused by fan cycling on the econdensre and not letting the TXV to stabilize. Try opeing up the band on the fan cycling controls.
First, check to see if the suction pressure is sort of laging the head pressure.
Ken
-
28-02-2009, 12:42 AM #4
-
28-02-2009, 12:44 AM #5
-
28-02-2009, 12:56 AM #6
Re: What will cause eva pressure fluctuate?
Last edited by Gary; 28-02-2009 at 01:07 AM.
-
28-02-2009, 01:16 AM #7
Re: What will cause eva pressure fluctuate?
-
28-02-2009, 02:00 AM #8
-
28-02-2009, 02:01 AM #9
-
01-03-2009, 12:18 PM #10
Re: What will cause eva pressure fluctuate?
A too big orifice
It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.
-
03-03-2009, 09:23 AM #11
Re: What will cause eva pressure fluctuate?
I have changed the TXV for several times, all new.
But there seems to be no effect, it's still hunting.
You guys have talked about insufficient air flow, or the condenser fan problem causing the condensing pressure hunting. But I have other system with the same evap air flow and the same condensing pressure. The cond air flow is from the same condensing fan .
-
03-03-2009, 10:09 AM #12
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,151
- Blog Entries
- 6
- Rep Power
- 36
Re: What will cause eva pressure fluctuate?
What is compressor model#, designed evaporation and condensation temperature, TXV model#, orifice#, actual evaporator air in temperature, condenser air in and out temperature?
-
04-03-2009, 01:28 AM #13
Re: What will cause eva pressure fluctuate?
How about giving us some readings of the fluctiation, air on, air off, system suction & discharge pressure, super heat, at the highest and lowest peak, whats the humidity level in the room.
Also does the TEV have an external equaliser if so have you made sure its not blocked or is it a power assembly.
Whats the room set point your trying to acheive, is it fresh air or does it recycle. how big is the room, whats the duty of the system.
We realy are just stabbing at a possible solution to your problem here, you need to give us more date so we can help.
-
05-03-2009, 02:56 AM #14
Re: What will cause eva pressure fluctuate?
Hi,coolments!
Here is the thing:
This unit has four compressors,each is a circuit. The four system s have the same cond temperature(50 degree), but different evap pressure. The indoor air pass the four evaporators sequentially, which makes the four evaporators evaporate at 13, 3, -3, -6 degree(from one to four system)
1,2 and 4 system run quite well and only the 3rd system's evap pressure fluctuates.
-
05-03-2009, 03:20 AM #15
Re: What will cause eva pressure fluctuate?
-
05-03-2009, 05:58 AM #16
Re: What will cause eva pressure fluctuate?
The 3rd system has one evaporator, two TXVs and one refrigerant distributors, which means the R22 was expanded by two TXVs and then enter the same distributor.
As for the other three circuit, they all have just one bigger TXV, would that be a cause of the fluctuation?
-
05-03-2009, 06:22 AM #17
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,151
- Blog Entries
- 6
- Rep Power
- 36
Similar Threads
-
Capillary Tube Characteristics
By Chef in forum FundamentalsReplies: 9Last Post: 10-03-2009, 01:03 PM -
Compressor loading, cooling, and range of operation.
By Air duster in forum FundamentalsReplies: 10Last Post: 02-04-2008, 08:39 AM -
Benji
By benji in forum Trouble ShootingReplies: 29Last Post: 30-01-2008, 01:25 PM -
Building a wine cabinet
By Rory in forum Technical DiscussionsReplies: 38Last Post: 13-07-2004, 08:28 PM