Results 1 to 1 of 1
Thread: indirect heating circuit
26-02-2009, 01:03 PM #1
We are planning to use the rejected heat from oil cooling on our screw compressors to warm a water storage vessel. We currently have a water/glycol circuit doing the cooling through a coil in the condenser. We are proposing to divert this heat to a simple indirect loop within the warm water cylinder to increase the temperature of the water prior to entering the boiler.
The glycol circuit is an 80mm stainless pipe with 7.8l/s flow with a maximum available 310kW of heat. The glycol will enter the heating loop at 41°C, leaving at 31°C.
In the worst case, the water entering the tank at 16l/s will be at 10°C.
Can anyone tell me how to calculate the surface area of the pipe doing the indirect heating to try and get the water to 31°C.
Incidentally, the tank will hold 28,000L and when the oil return temperature is too high the glycol circuit will simply revert back to being cooled in the condenser circuit.