Thread: Drinking Fountain / Water Cooler
26-02-2009, 09:24 AM #1
Good day! RE people, i believe everyone or if not most of the people here knows what a Drinking Fountain is. Im making one and I have made a few calculations already and i don't know if i'm on the right path i just wanna hear some side comments and/or a few suggestions in obtaining the following:
1. Compressor specification and capacity (I have two suppliers ready: Danfoss and Tecumseh)
2. Air-Cooled Condenser specification (Im planning of using 5/16 copper tube, how much FPI, Fin Length, Number of tube face, No. of rows etc. to use?). Fan Selection
3. Evaporator Length (im using 5/16 copper tube too)
4. Capillary Tube Length (im using 0.036 in)
Here it is:
This is the part were water is stored to be cooled regulated by a solenoid valve:
Design Conditions
Ambient Temp: 32 ºC
Inlet Water Temp (T1): 29 ºC
Output Water Temp (T2): 5 ºC
Cooling Tank Selection
Outside diameter (do): 4-in
Tank length (L): 12-in
Critical pressure (Pcr): 150 psi
Thickness (t): ?
Capacity of stainless tube (V): ?
Inside diameter (di): ?
Pcr = (50,200,000 (t/do)^3) / 3
Pcr = (50,200,000 (t/4)^3) / 3
t = 0.0831 in or 2.111 mm
V = π(di)2 L / 4
V = π(3.8338)2 (12) / 4
V = 138.53 cu. in or 2.27 Li
Cooling System Design
Materials
Stainless tube: 0.0831 in x 4-in dia. X 12 in
Copper tube: 5/16 in dia. x L?
Styropore insulation: 1.0 in x 6-in dia. X 14 in
Data
Specific heat of water (Cp): 4.187 KJ/Kg-ºC
Specific heat of SS (Cs): 0.450 KJ/Kg-ºC
Water density: 1000 kg/cu.mtr
SS density: 8.03 g/cu.cm = 0.1316 kg/cu.in
Water Inlet temp
Volume conversion
138.53 cu.in (1 cu.ft)(1cu.mtr)
(1728 cu.in)(35.29 cu. cu.ft)
= 2.27 x 10 –3 cu mtr
Mass of water (Mw)
Mw = 2.27 x 10 –3 cu.mtr (1000 kg/cu.mtr)
Mw = 2.27 kg
Load from water
Qw = Mw Cp (T1 – T2)
Qw = (2.27)(4.187)(29 – 5)
Qw = 228.11 KJ
Volume of stainless steel
Vs1 = 0.26 cu.in
Vs2 = 2 {[π (4)2 /4] (0.0831)}
Vs2 = 2.1 cu.in
Vs = Vs1 + Vs2
Vs = 0.26 + 2.1
Vs = 2.36 cu.in
Mass of stainless Steel (Mss)
Ms = Density of SS x Volume of SS
Ms = (0.1316)(2.36)
Ms = 0.311 Kg
Load from stainless tube
Qs = Ms Cs (T1 – T2)
Qs = (0.31)(0.450)(29 - 5)
Qs = 3.348 KJ
Calculated load from temperature difference between ambient and water condition inside the tank:
Q1 = 4.7116 Watts
Q1 = 4.7166 J/s
Q1 = 0.0047166 KJ/s
@ 60 secs
Q1 = 0.3 KJ
Total Load
Q = Qwater + Qstainless + Q1
Q = 228.11 + 3.348 + 0.3
Q = 231.8 KJ = 219.72 BTU : Is this correct or i am missing something here? i have a feeling that my tabulated total load is somewhat small
26-02-2009, 11:48 AM #2
Re: Drinking Fountain / Water Cooler
what i think you have missed is the flow rate of the water passing through the drinking fountain. The calculations are fine if the water in the heat exchanger is static so the next thing to calculate (guestimate) is how many litres /min flow rate ...how many water changes inside heat exchanger /hr and also how quickly is the water to be cooled.hope this helps a bit
10-03-2009, 01:53 AM #3
hi there! thanks for you comment, i was wondering on that part too considering that my reference(s) books are stating the flow rate. and yes, you are right, the water is not static, i think it is even safer to assume that from time to time cold water is drawn from the drinking fountain. anyway, i don't really know what to put in here because of the varying flow rate of water here in our country (any suggestions?) or perhaps it would be best to assume a certain flow rate for this part?
I think the cooling rate can be calculated from the specifications given by the compressor manufacturer, 30 - 60 mins cooling time perhaps?
10-03-2009, 06:38 PM #4
If you want a fixed water flow rate then install flow regulation devices to maintain your desired flow rate.
pure water from air
By Lc_shi in forum New TechnologiesReplies: 32Last Post: 26-02-2009, 12:25 PM -
Ultra compact water cooler for Tig Welding?
By bjamesw in forum FundamentalsReplies: 7Last Post: 28-12-2008, 03:04 PM -
Water Cooler Design
By Rayin in forum FundamentalsReplies: 4Last Post: 14-03-2007, 06:17 AM -
water cooler
By amaryta in forum New TechnologiesReplies: 6Last Post: 11-09-2006, 10:56 PM -
Building a wine cabinet