    Drinking Fountain / Water Cooler



    Good day! RE people, i believe everyone or if not most of the people here knows what a Drinking Fountain is. Im making one and I have made a few calculations already and i don't know if i'm on the right path i just wanna hear some side comments and/or a few suggestions in obtaining the following:

    1. Compressor specification and capacity (I have two suppliers ready: Danfoss and Tecumseh)

    2. Air-Cooled Condenser specification (Im planning of using 5/16 copper tube, how much FPI, Fin Length, Number of tube face, No. of rows etc. to use?). Fan Selection

    3. Evaporator Length (im using 5/16 copper tube too)

    4. Capillary Tube Length (im using 0.036 in)



    Here it is:

    This is the part were water is stored to be cooled regulated by a solenoid valve:



    Design Conditions


    Ambient Temp: 32 ºC
    Inlet Water Temp (T1): 29 ºC
    Output Water Temp (T2): 5 ºC


    Cooling Tank Selection

    Outside diameter (do): 4-in
    Tank length (L): 12-in
    Critical pressure (Pcr): 150 psi
    Thickness (t): ?
    Capacity of stainless tube (V): ?
    Inside diameter (di): ?


    Pcr = (50,200,000 (t/do)^3) / 3

    Pcr = (50,200,000 (t/4)^3) / 3

    t = 0.0831 in or 2.111 mm


    V = π(di)2 L / 4

    V = π(3.8338)2 (12) / 4

    V = 138.53 cu. in or 2.27 Li



    Cooling System Design

    Materials


    Stainless tube: 0.0831 in x 4-in dia. X 12 in
    Copper tube: 5/16 in dia. x L?
    Styropore insulation: 1.0 in x 6-in dia. X 14 in


    Data

    Specific heat of water (Cp): 4.187 KJ/Kg-ºC
    Specific heat of SS (Cs): 0.450 KJ/Kg-ºC
    Water density: 1000 kg/cu.mtr
    SS density: 8.03 g/cu.cm = 0.1316 kg/cu.in
    Water Inlet temp


    Volume conversion

    138.53 cu.in (1 cu.ft)(1cu.mtr)
    (1728 cu.in)(35.29 cu. cu.ft)

    = 2.27 x 10 –3 cu mtr




    Mass of water (Mw)

    Mw = 2.27 x 10 –3 cu.mtr (1000 kg/cu.mtr)

    Mw = 2.27 kg


    Load from water

    Qw = Mw Cp (T1 – T2)

    Qw = (2.27)(4.187)(29 – 5)




    Qw = 228.11 KJ





    ========================================

    Volume of stainless steel

    Vs1 = 0.26 cu.in


    Vs2 = 2 {[π (4)2 /4] (0.0831)}

    Vs2 = 2.1 cu.in


    Vs = Vs1 + Vs2

    Vs = 0.26 + 2.1

    Vs = 2.36 cu.in



    Mass of stainless Steel (Mss)



    Ms = Density of SS x Volume of SS



    Ms = (0.1316)(2.36)

    Ms = 0.311 Kg




    Load from stainless tube



    Qs = Ms Cs (T1 – T2)



    Qs = (0.31)(0.450)(29 - 5)



    Qs = 3.348 KJ

    ---




    Calculated load from temperature difference between ambient and water condition inside the tank:

    Q1 = 4.7116 Watts

    Q1 = 4.7166 J/s

    Q1 = 0.0047166 KJ/s


    @ 60 secs


    Q1 = 0.3 KJ



    Total Load


    Q = Qwater + Qstainless + Q1

    Q = 228.11 + 3.348 + 0.3

    Q = 231.8 KJ = 219.72 BTU : Is this correct or i am missing something here? i have a feeling that my tabulated total load is somewhat small





  2. #2
    Join Date
    Dec 2008
    Location
    Australia
    Age
    61
    Posts
    44
    Rep Power
    0

    Re: Drinking Fountain / Water Cooler

    what i think you have missed is the flow rate of the water passing through the drinking fountain. The calculations are fine if the water in the heat exchanger is static so the next thing to calculate (guestimate) is how many litres /min flow rate ...how many water changes inside heat exchanger /hr and also how quickly is the water to be cooled.hope this helps a bit

  3. #3
    Join Date
    Apr 2008
    Location
    Philippines
    Posts
    8
    Rep Power
    0

    Re: Drinking Fountain / Water Cooler

    hi there! thanks for you comment, i was wondering on that part too considering that my reference(s) books are stating the flow rate. and yes, you are right, the water is not static, i think it is even safer to assume that from time to time cold water is drawn from the drinking fountain. anyway, i don't really know what to put in here because of the varying flow rate of water here in our country (any suggestions?) or perhaps it would be best to assume a certain flow rate for this part?

    I think the cooling rate can be calculated from the specifications given by the compressor manufacturer, 30 - 60 mins cooling time perhaps?

  4. #4
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Drinking Fountain / Water Cooler

    If you want a fixed water flow rate then install flow regulation devices to maintain your desired flow rate.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

Similar Threads

  1. pure water from air
    By Lc_shi in forum New Technologies
    Replies: 32
    Last Post: 26-02-2009, 12:25 PM
  2. Ultra compact water cooler for Tig Welding?
    By bjamesw in forum Fundamentals
    Replies: 7
    Last Post: 28-12-2008, 03:04 PM
  3. Water Cooler Design
    By Rayin in forum Fundamentals
    Replies: 4
    Last Post: 14-03-2007, 06:17 AM
  4. water cooler
    By amaryta in forum New Technologies
    Replies: 6
    Last Post: 11-09-2006, 10:56 PM
  5. Building a wine cabinet
    By Rory in forum Technical Discussions
    Replies: 38
    Last Post: 13-07-2004, 08:28 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •