    Hi, we want to design a new Air to water split heat pump, we have three questions:

    1.The compressor should be located in the outside unit or inside unit? Which one is better?

    2.Can we place the buffer tank in the inside unit?

    3.we want to design a double jacketed hot water tank , which means that it consists of two separate tanks. The hot water is heated in the inner jacket.The inside tank is 200L,the outside tank is 300L, is it ok?



  2. #2
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Air to water split heat pump design

    Quote Originally Posted by ginger jiang View Post
    Hi, we want to design a new Air to water split heat pump, we have three questions:

    1.The compressor should be located in the outside unit or inside unit? Which one is better?
    Outside. Reasoning:
    Noise is generated outside
    Smaller dimensions of indoor unit
    Possibility to install more then one indoor unit

    2.Can we place the buffer tank in the inside unit?
    Yes you can, but that increase dimensions of indoor unit.

    3.we want to design a double jacketed hot water tank , which means that it consists of two separate tanks. The hot water is heated in the inner jacket.The inside tank is 200L,the outside tank is 300L, is it ok?
    Why you dont use simple water tank with conventional spiral tube heat exchanger?

  3. #3
    Join Date
    Feb 2009
    Location
    Guangzhou,China
    Age
    42
    Posts
    10
    Rep Power
    0

    Re: Air to water split heat pump design

    we want "tank in tank "because we think it's more efficient---the heating area is bigger than spiral tube.

  4. #4
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Air to water split heat pump design

    Quote Originally Posted by ginger jiang View Post
    we want "tank in tank "because we think it's more efficient---the heating area is bigger than spiral tube.
    Did you make calculation on surface area of cylindrical tank of 200L and say 10m of pipe of 1" diameter?

    Cylinder of 0,4m height and 0,4m radius has volume of cca 200L and active area (in other cylinder active is only mantle and bottom area) of cca 1,5m^2.

    Pipe of 1" diameter and 10m lenght roled in spiral (8 windings of 0,2m radius) have active area of 1.59m^2.
    Last edited by nike123; 26-02-2009 at 08:39 AM.

Similar Threads

  1. Sensible Heat Factor / capacity of Inverter split Systems at part load?
    By Greengrocer in forum Technical Speculations
    Replies: 31
    Last Post: 09-02-2009, 04:57 PM
  2. water source heat pump
    By gramcor in forum Air Conditioning
    Replies: 1
    Last Post: 11-03-2008, 12:06 AM
  3. chilled water pump design
    By afeef in forum Fundamentals
    Replies: 5
    Last Post: 16-09-2005, 12:06 AM
  4. Water Source Heat Pump
    By aliugur in forum Fundamentals
    Replies: 1
    Last Post: 02-06-2002, 03:24 PM
  5. R134a <-> liquid heat exchanger design
    By DaBit in forum Technical Speculations
    Replies: 19
    Last Post: 10-05-2002, 08:36 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •