    Mitsubishi FDTWJ56HKXE2 - (Fan Motor)



    I have a problem with a mitsubishi indoor unit (vr system) - model - fdtwj56hkxe2 - the fan motor rounds from the wrong way , instead of blowing air into the room from the louvers and sucking air from the filters beneath the fan motor , it blows air from the filters and sucks from the air louvers - the motor uses 1 phase of source power and i can't find what it is . The strange is that i have changed and the indoor pcb and the fan motor and it still works wrong .... Help ???



  2. #2
    Join Date
    Dec 2001
    Location
    UK
    Posts
    137
    Rep Power
    23

    Re: Mitsubishi FDTWJ56HKXE2 - (Fan Motor)

    Check the fan capacitor. This will be plugged into the pcb and is either not connected or is itself faulty.
    Brit

  3. #3
    Join Date
    Oct 2008
    Location
    Australia
    Posts
    210
    Rep Power
    16

    Re: Mitsubishi FDTWJ56HKXE2 - (Fan Motor)

    definatly capacitor

  4. #4
    Join Date
    Dec 2006
    Location
    Mansfield
    Age
    57
    Posts
    231
    Rep Power
    0

    Re: Mitsubishi FDTWJ56HKXE2 - (Fan Motor)

    I have to agree, capacitor!


    PP

  5. #5
    Join Date
    Feb 2009
    Location
    Athens
    Age
    40
    Posts
    5
    Rep Power
    0

    Re: Mitsubishi FDTWJ56HKXE2 - (Fan Motor)

    thanks a lot , i will check it out , i thought that it will probably be a capacitor problem , i putted on a new one but it didn't worked coeectly , i will try to change the connection of the capacitor . I saw to the pcb drawings that it has 4 - 5 options of capacitor installation .... Thanks a lot again !!!!Rasoulis M. From Hellas . . .

Similar Threads

  1. 1ph motor instead of 3 ph motor.
    By SPBDASAN in forum Electrical
    Replies: 1
    Last Post: 20-02-2009, 07:56 AM
  2. Compressor loading, cooling, and range of operation.
    By Air duster in forum Fundamentals
    Replies: 10
    Last Post: 02-04-2008, 08:39 AM
  3. help with testing 3 phase comp
    By mat in forum Fundamentals
    Replies: 7
    Last Post: 19-01-2007, 09:03 AM
  4. locked rotor amps (LRA)
    By vinod in forum Technical Discussions
    Replies: 16
    Last Post: 09-09-2006, 12:50 AM
  5. Fan motor over heating & Shuting down.
    By Rookie in forum Domestic
    Replies: 15
    Last Post: 30-06-2005, 11:21 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •