    Me msh-18nv



    Went to a Mitsubishi Electric Hight wall split today Model - MSH-18NV. Now i couldnt gain access to the condensing unit but i suspect the unit short on refrigerant.

    What was happening i would run the unit on cooling setpoint 16 room temp 25 and the unit would start cooling albeit not well. Then after 10secs the Reversing valve would click and unit would run heating for about 10secs then compressor would shut off.

    Now my question is, is this normal? Is the unit defrosting the indoor coil due to below specfied coil temp?

    Im not to familar with these units and id like a bit of a heads up before i go back. I think its a gas issue but just making sure. Also if anyone has a service manual that would be great as well.

    Thanx
    Last edited by rude; 23-02-2009 at 01:00 PM.



  2. #2
    Join Date
    Dec 2008
    Location
    Isle of Man
    Age
    55
    Posts
    42
    Rep Power
    0

    Re: Me msh-18nv

    Hi,
    How can you tell that the reversing valve has energised? Sounds to me like it's got virtually no gas in it, it's just circulating ambient air (25 degrees) until it trips on LP.

  3. #3
    Join Date
    Oct 2008
    Location
    Australia
    Posts
    210
    Rep Power
    16

    Re: Me msh-18nv

    i can feel the evap pipes get warm.

  4. #4
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Me msh-18nv

    There could be a problem with the de-icer board but sounds odd.

    Service Manual here if wanted, 3.18MB

    http://es.mehvac.com/UploadedFiles/R...0059123856.PDF
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  5. #5
    Join Date
    Oct 2008
    Location
    Australia
    Posts
    210
    Rep Power
    16

    Re: Me msh-18nv

    Thank you very much! I suppose when i gain access to condensing unit i can check the gas/boards etc

  6. #6
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Me msh-18nv

    Also, it depends on the type of 4-port valve, but low gas pressures can give those valves funny actions.