    Foster walk in freezer



    Help required,

    Working on a foster walk in freezer offshore and am ready to charge the sytem but i have no scales.

    the system requires 0.980kg of R404a to be added which i will have to do by hand.

    Am not sure what the LP running pressure should be.
    looking for a rough running pressure i can work to

    note...No access fitting to HP


    Foster

    Model:SP301LW

    Can anyone help



  2. #2
    Join Date
    Jul 2008
    Location
    London
    Posts
    848
    Rep Power
    17

    Re: Foster walk in freezer

    the kitchens must have a weighing machine?

    otherwise yurn the bottle upsidedown and count one mississippi for 50gms. Then charge to the frost line. Get it down to temp let it cut out on the stat twice to make sure it's settled and see it ice back -assuming it is a cap system a tev one will have a s/g
    Last edited by multisync; 22-02-2009 at 10:20 PM.

  3. #3
    Join Date
    Aug 2008
    Location
    UK
    Posts
    19
    Rep Power
    0

    Re: Foster walk in freezer

    Good point,

    But ive checked and they dont sadly.

  4. #4
    Join Date
    Mar 2004
    Location
    UK
    Posts
    625
    Rep Power
    21

    Re: Foster walk in freezer

    Hi charge to 1 bar

    Regards Bernard

  5. #5
    Join Date
    Aug 2008
    Location
    UK
    Posts
    19
    Rep Power
    0

    Re: Foster walk in freezer

    Thanks bernard i do have a comparator but i am unsure how to use it.

    I take its the vapour were looking at, So slide it along to 1 bar looking at the pabs/Pe or at the top we have psia? psig which one would it be ? and that would give you your running temp.

  6. #6
    Join Date
    Mar 2004
    Location
    UK
    Posts
    625
    Rep Power
    21

    Re: Foster walk in freezer

    Hi

    Use PSIG,with cap tube I always take the temp I want to acheive which in your case is -21 then add -12 = -33 which is approx 1 bar. Charge very slowly ensuring you don,t have liquid back on compressor.This all depends on condition of coil.I find this better than using scales as a lot of the time the weight is in correct from manufacturer.

    Regards Bernard

  7. #7
    Join Date
    May 2006
    Location
    Isle of Wight, Uk
    Age
    47
    Posts
    425
    Rep Power
    20

    Re: Foster walk in freezer

    Make sure the condenser coil is clean - give it a good wash, it will make your life easier.

    Andy

  8. #8
    Join Date
    Mar 2007
    Location
    England
    Posts
    34
    Rep Power
    0

    Re: Foster walk in freezer

    also try to charge with the front cover on as much as possible with these foster units too if not pressure readings will not be accurate

Similar Threads

  1. walk in freezer
    By ail in forum Refrigerants
    Replies: 8
    Last Post: 30-11-2009, 12:44 AM
  2. walk in freezer
    By tonto33 in forum Commercial
    Replies: 4
    Last Post: 05-10-2009, 09:12 PM
  3. help!! getting beat up by a walk in freezer
    By avalanche in forum Commercial
    Replies: 12
    Last Post: 05-12-2008, 03:56 AM
  4. walk in freezer refrigeration sizing?
    By trammd in forum Technical Discussions
    Replies: 10
    Last Post: 02-11-2006, 12:56 PM
  5. It's snowing in my walk in freezer!
    By Matt in forum Commercial
    Replies: 19
    Last Post: 14-10-2006, 07:07 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •