    Pull down temp new cold store



    Appreciate if anyone give their opinion on whats the best way to pull the temperature down on a brand new cold storage facility.

    Room temperature today is @ +25c under construction
    End result needed -22c

    My idea is

    Days 1-3 +4c
    Days 4-10 +2c
    Days 11-15 0c
    From here drop 2 to 3 deg per day until room temperature required achieved.

    During the pull down authorized access will be controlled



  2. #2
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Pull down temp new cold store

    I suggest 5K per day except between +2°C and -2°C temperature, where it should be slower, for example 2K per day. That is how I was taught. But, that could depend on size. Bigger the size, slower shake-down.

  3. #3
    colinc's Avatar
    colinc Guest

    Re: Pull down temp new cold store

    The size of the room is 16000 pallets

  4. #4
    Join Date
    Feb 2008
    Location
    Buenos Aires
    Posts
    8
    Rep Power
    0

    Re: Pull down temp new cold store

    We are doing big walk in coolers and freezer since 50 years ago
    we had experience in this subjet and solve the problems cooling as low as posible. Normally 10 to 15 days
    A big camera problem is if cooling is quick, the superficial superficie is soft and when the circulation of lift truck start, there is a lot of powder. . We use in the concrete and aerator and we applied a special liquid over the surface, for close the cell. If you are interesed we can send the namecomponents that our supplier included in the concrete, also the name of components of sealers,
    Paint over superficie is lost time.
    Normally we use do a very smooth surface using a helicopter
    Luisarce
    Arceyasoc@arnet.com.ar

Similar Threads

  1. Construction of new Cold Store
    By lalthomas in forum System Optimization
    Replies: 23
    Last Post: 19-04-2009, 02:01 AM
  2. Expansion Joints in the cold store floor
    By smpsmp45 in forum NH3
    Replies: 2
    Last Post: 17-05-2008, 07:47 AM
  3. Compressor loading, cooling, and range of operation.
    By Air duster in forum Fundamentals
    Replies: 10
    Last Post: 02-04-2008, 08:39 AM
  4. cold room temp & the product temp
    By smpsmp45 in forum NH3
    Replies: 9
    Last Post: 21-09-2007, 11:46 PM
  5. Recip Vs Scroll compressors for Low temp cold store
    By smpsmp45 in forum Industrial Compressors
    Replies: 9
    Last Post: 23-06-2007, 12:47 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •