21-02-2009, 02:21 PM #1
Samsung AQB 18 Vicace Tripping Out RCD
Hello,
Please could any of you help me, I am having problems with the above unit tripping the 30mA RCD as soon as the power is switched on. The unit is brand new and this happened on the initial start up. I have never wired any of these units up before. Does the power unit have a high earth current leakage?
Cheers and thanks for any help
BondingBill
-
21-02-2009, 05:20 PM #2
Re: Samsung AQB 18 Vicace Tripping Out RCD
In general air conditioning systems are not included on circuits fed by RCDs.
We've had discussions on this before, I'll have a search around for you.
[edit] Have a look here, post 11.
http://www.refrigeration-engineer.co...tripping+powerLast edited by Brian_UK; 21-02-2009 at 05:27 PM.
Brian - Newton Abbot, Devon, UK
Retired March 2015
-
21-02-2009, 08:23 PM #3
Re: Samsung AQB 18 Vicace Tripping Out RCD
Many thanks Brian for your help, the only problem is that this unit has been fitted on a camping park (cabins) and has to be protected by a 30mA RCD by IEE regs. The heat pump was fitted without my knowledge, otherwise I would of advised the customer against buying it, but as he has now fitted it I have to try and find away to get it working. Maybe I can wire a seperate 100mA RCD just for the unit. Do you know of anyone who's had any success fitting an 100mA RCD on this unit
Thanks again, I will let you know how I get on.
Cheers Bondingbilll
-
21-02-2009, 11:02 PM #4
Re: Samsung AQB 18 Vicace Tripping Out RCD
This might be a silly question BondingBil, but what's the full load amps on the A/C and what's the amp rating on the RCD?
You're not just overloading the breaker are you?
-
22-02-2009, 12:19 AM #5
Re: Samsung AQB 18 Vicace Tripping Out RCD
Obvious, but have you checked the unit is wired correctly? No crossed wires, etc.
Out of intrest, "Why would you have advised against buying it" ?
These units are NOT meant to be self install by the way!
-
22-02-2009, 11:57 AM #6
Re: Samsung AQB 18 Vicace Tripping Out RCD
hi , max load 12 amps , mcb 20 , rcd rated at 45 amps with a 30m mA trip.
It is the rcd that is tripping not the mcb. I think it is something to do with the filters in the power supply unit in the heat pump , leaking it down to earth, cheers
-
22-02-2009, 12:25 PM #7
Re: Samsung AQB 18 Vicace Tripping Out RCD
hi, this job is for the heating engineer that i do contract work for, he has fitted it in his holiday lodge which is controlled by IEE camping park regulations i;e has to be protected by a 30mA RCD and total load for the lodge is 20amps no more and this is the reason why I would have recomended him not to buy it. His work force have been trained on heat pumps and this was the first one he had fitted and he was trying this one out for his own purpose. He had an independent refrigeration engineer on site to commission it.
cheers
-
22-02-2009, 01:22 PM #8
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,151
- Blog Entries
- 6
- Rep Power
- 36
Re: Samsung AQB 18 Vicace Tripping Out RCD
There are special RCD-s made for that purpose. They are called B type (It exsist 3 types:A,B and AC). Manufacturer is ABB. Model# is F200 B
]http://hvacity.danfoss.com/pdf_files/rcd.pdfLast edited by nike123; 22-02-2009 at 02:40 PM.
-
22-02-2009, 06:13 PM #9
Re: Samsung AQB 18 Vicace Tripping Out RCD
If there is already a fridge running on the power network this will bring the current leakage very close to tripping point,
A new unit sould run within the 30ma limit, older units the insulation started to break down in the comp and the oil isn't resisting the path of current flow as it did new.!
-
22-02-2009, 09:03 PM #10
Re: Samsung AQB 18 Vicace Tripping Out RCD
HI , yes there is a fridge on the network, I will be calling back to this job on wednesday , I will test the complete installation and try it with all other appliances disconnected,
thanks for your help B/B
-
23-02-2009, 09:15 AM #11
Re: Samsung AQB 18 Vicace Tripping Out RCD
Hi BondingBill, are you saying that everything in the cabin goes through the same RCD?
-
26-02-2009, 05:01 AM #12
Re: Samsung AQB 18 Vicace Tripping Out RCD
if the system is inverter it shouldnt be tripping out as soon as its running even if there is a fridge running.
INverters dont draw full current at start up they wind up slowly.
If its a fixed speed unit then yes it will run at full possibly a little more to get it going.
Have you actually switched the unit onto operation when it trips or just at the mains?
-
26-02-2009, 10:53 PM #13
-
06-03-2009, 10:47 AM #14
Re: Samsung AQB 18 Vicace Tripping Out RCD
sorry for the late reply. NO it isnt the overload its the 30ma local rcd and also the 300ma upstream rcd that is also tripping. I have tested insulation to earth on the unit and i get a very low reading, it must be a faulty unit. but up till now i can not convince the service people it is faulty. im now waiting for their reply on monday.
p.s the unit is situated 120 miles away in the lake district.
THanks for your help
bonding bill