Thread: humidifier load calculations
20-02-2009, 03:07 PM #1
Does anyone have an equation to kg/hr from an electrode boiler to kj/kg or kw.
I look forward to any ideas
Quidvis Recte Factum Quamvis Humile Praeclarum.
Latine dictum, sit altum videtur.
Si hoc comprehendere potes, gratias age magistro Latinae.
20-02-2009, 07:49 PM #2
Re: humidifier load calculations
For 1kg/hr of vapor you need 0.725kW of energy.
23-02-2009, 08:37 AM #3
thanks for your reply Narkom
I believe that the 0.725kw is the electrical load to produce 1kg of water vapor in one hour but what I need is to calculate the change in enthalpy in the air due to the super heated vapor being introduced.
If you could help me further I would be thankful.Quidvis Recte Factum Quamvis Humile Praeclarum.
23-02-2009, 01:05 PM #4
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,151
- Blog Entries
- 6
- Rep Power
- 36
23-02-2009, 04:11 PM #5
Thanks Nike
Thats the sort of thing I was looking for
I thought I'd already checked the toolbox. I must be getting old.Quidvis Recte Factum Quamvis Humile Praeclarum.