    TRASH101's Avatar
    TRASH101 is offline Veteran Poster I am starting to push the Mods: of RE
    Mar 2007
    394
    humidifier load calculations
    Does anyone have an equation to kg/hr from an electrode boiler to kj/kg or kw.
    I look forward to any ideas
    Quidvis Recte Factum Quamvis Humile Praeclarum.
    Aug 2007
    Russia
    138
    Re: humidifier load calculations
    For 1kg/hr of vapor you need 0.725kW of energy.
    TRASH101's Avatar
    Mar 2007
    394
    thanks for your reply Narkom
    I believe that the 0.725kw is the electrical load to produce 1kg of water vapor in one hour but what I need is to calculate the change in enthalpy in the air due to the super heated vapor being introduced.
    If you could help me further I would be thankful.
    Split Croatia
    6,151
    Quote Originally Posted by TRASH101 View Post
    http://www.engineeringtoolbox.com/en...air-d_683.html
    TRASH101's Avatar
    Mar 2007
    394
    Thanks Nike
    Thats the sort of thing I was looking for
    I thought I'd already checked the toolbox. I must be getting old.
  1. Cooling Load Calculations
    By hamidpia in forum Tools and Calculators
    Last Post: 05-02-2009, 08:57 PM
  2. Heat Load Calculations
    By tjk2007 in forum Tools and Calculators
    Last Post: 11-05-2008, 02:24 AM
  3. Compressor loading, cooling, and range of operation.
  4. Heat Load Calculations - Part L Building Regs
    By Refrigerologist in forum Tools and Calculators
    Last Post: 12-03-2008, 09:53 AM
  5. Soap Plant Load Calculations
    By tjk2007 in forum Fundamentals
    Last Post: 25-11-2007, 05:59 AM
