thermostatic expansion valve sizing
hi all,
i have a 1TR r22 air conditioning unit for my experiment in college. it has a capillary tube & an automatic expansion valve for the expansion purpose. we have to install a TEV to control the superheat in the system. Problem is that we are not able to find a TEV for a 1 TR unit. the lowest i found is Pr no 2059, DANFOSS, it is sized for a 4.5TR unit. Is it ok to use this valve for our purpose?
-
19-02-2009, 12:31 PM #2
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,151
- Blog Entries
- 6
- Rep Power
- 36
Re: thermostatic expansion valve sizing
No, you have Danfoss T2/TE2 valves with orifices which will match your system capacity from 0,15 to 4,5 TR.
For your case, TX 2/TEX 2-1.0 with orifice no 2 is probably best.
http://rc.danfoss.com/TechnicalInfo/...CPDAA0A302.pdfLast edited by nike123; 19-02-2009 at 12:33 PM.
-
03-03-2009, 03:22 PM #3
Re: thermostatic expansion valve sizing
hey thanks nike123, i purchased the valve that you mentioned. I learnt a few practical things , while searching the shops & I realize how stupid my first post looks. But as your signature says, its just easy:-p.
thanks again
Similar Threads
-
Actual Expansion Valve Process
By AastroGuru in forum FundamentalsReplies: 11Last Post: 03-02-2009, 09:53 AM -
Thermostatic Expansion Valve TXV - Block Type
By AastroGuru in forum FundamentalsReplies: 10Last Post: 24-12-2008, 09:53 AM -
Setting of Hand expansion valve
By Iceehot in forum NH3Replies: 7Last Post: 10-09-2008, 01:25 AM -
Need Divine Intervention - plugged drier or expansion valve?
By archibaldtuttle in forum Trouble ShootingReplies: 4Last Post: 08-06-2008, 06:52 PM -
Expansion Valve Sizing
By cristopher_uy in forum Technical SpeculationsReplies: 2Last Post: 26-11-2007, 10:39 PM