    Jan 2008
    India
    36
    8
    thermostatic expansion valve sizing
    hi all,
    i have a 1TR r22 air conditioning unit for my experiment in college. it has a capillary tube & an automatic expansion valve for the expansion purpose. we have to install a TEV to control the superheat in the system. Problem is that we are not able to find a TEV for a 1 TR unit. the lowest i found is Pr no 2059, DANFOSS, it is sized for a 4.5TR unit. Is it ok to use this valve for our purpose?
    Split Croatia
    57
    6,151
    36
    Re: thermostatic expansion valve sizing
    Quote Originally Posted by ank_gl View Post
    hi all,
    No, you have Danfoss T2/TE2 valves with orifices which will match your system capacity from 0,15 to 4,5 TR.
    For your case, TX 2/TEX 2-1.0 with orifice no 2 is probably best.
    http://rc.danfoss.com/TechnicalInfo/...CPDAA0A302.pdf
    Jan 2008
    India
    36
    8
    Thumbs up Re: thermostatic expansion valve sizing
    hey thanks nike123, i purchased the valve that you mentioned. I learnt a few practical things , while searching the shops & I realize how stupid my first post looks. But as your signature says, its just easy:-p.
    thanks again
  1. Actual Expansion Valve Process
    By AastroGuru in forum Fundamentals
    Last Post: 03-02-2009, 09:53 AM
  2. Thermostatic Expansion Valve TXV - Block Type
    Last Post: 24-12-2008, 09:53 AM
  3. Setting of Hand expansion valve
    By Iceehot in forum NH3
    Last Post: 10-09-2008, 01:25 AM
  4. Need Divine Intervention - plugged drier or expansion valve?
    By archibaldtuttle in forum Trouble Shooting
    Last Post: 08-06-2008, 06:52 PM
  5. Expansion Valve Sizing
    By cristopher_uy in forum Technical Speculations
    Last Post: 26-11-2007, 10:39 PM