Thread: Solenoid valve diagnostics
07-03-2009, 01:31 PM #1
Hi, I have a commercial refrigerating unit with dual cooling zones, 1 a wrapped cold bn and the other a refrigerator space. The 2 are controlled with txv's and solenoid valves. I believe one of the valves are leaking when closed causing repeated pump don cycles. Is there an easy way to find which solenoid valve is leaking through?
07-03-2009, 05:11 PM #2
Re: Solenoid valve diagnostics
Check the valve for temperature drop across it, it should be fairly obvious if it is passing!
08-03-2009, 10:48 AM #3
Good point from silhouette,you could also.
If individual l.p. switches are fitted?
which I assume is the case?
Try metering out or just watching which of them activates first?
It depends on your systems, but is there not a service port.
Where you can observe the individual rise in pressure?
08-03-2009, 12:34 PM #4
thanks guys, I didnt think bout the temp drop from the liquid flashing through the valve. I apreciate it. And only one low pres switch controlling the condenser but a good thought. Thanks Griz
08-03-2009, 02:16 PM #5
08-03-2009, 04:29 PM #6
dual etc's
08-03-2009, 08:15 PM #7
If the above diagnostics don't find the offending item, strip the valves and inspect the diaphram faces, if a piece of swarf or simillar has passed thru the valve, then there could be scratches on the teflon surface. The tinyest of scratches can cause the valve to pass. Using a bright light and mag glass will help with inspecting the surfaces. Then replace damaged diaphram and internal parts for an effective repair.
Reality is an elusion created by alcohol deficiency. Quaff and enjoy. [Yorkshire, UK]
08-03-2009, 10:39 PM #8
Drier, Sight Glass, Solenoid valve , which order?
By Drew in forum CommercialReplies: 16Last Post: 16-06-2010, 05:43 PM -
Liquid solenoid valve mystery
By mohamed khamis in forum ElectricalReplies: 20Last Post: 04-08-2008, 08:59 PM -
optimum defrost gas solenoid valve setting question
By racknovice in forum Supermarket RefrigerationReplies: 3Last Post: 14-12-2007, 06:49 AM -
Working of Solenoid Valve
By Mukesh in forum CommercialReplies: 25Last Post: 22-09-2006, 01:18 PM