Results 1 to 8 of 8
18-02-2009, 07:17 PM #1
Liquid in compressor when charging
Im recharging a water chiller system, but the only valve on the HP side is after the compresspr but before the condensor so is not actually on the liquid line. Im charging as a liquid with the compressor off but im worried about filling the compressor with liquid. What i would like to know do semi-hermetic compressors have valves to on the discharge outlet to prevent this from happening.
Any response would be much appreciated
18-02-2009, 08:28 PM #2
Re: Liquid in compressor when charging
are there no valves on the reciever ?? charging it up through the discharge valve should be o/k as the pressure should push against the discharge valves stoping it filling up with liquid,but this can depend on the design i suppose, anyway to be sure when finished leave it off but with the crankcase heater on over night,
18-02-2009, 08:43 PM #3
Even with the CC heater on overnight, I would worry about liquid sitting on the head/valve plate, or even findings its way into the compression chamber, and causing damage in that first stroke. May be a bit late for you, but I would have added my own charging port in the liquid and/or suction line while the gas was out.
"I'm anaspeptic, frasmotic, even compunctuous to have caused you such pericombobulation."
18-02-2009, 09:58 PM #4
sorry should of said, there is no liquid receiver. I had planned to leave over night to allow the crankcase heater to boil off any liquid that may have entered the compresser.
Thanks for the advice
18-02-2009, 10:33 PM #5
I`ve done this many times. I used to use a kwikcharger that allows the liquid to partially vapourise thus minimizing the possibility of liquid entering the compressor. I say "used to use" because it went the same way as all my other gear when my van was nicked. Now I use the sight glass in the gauge manifold throttling back the refrigerant valve control the flow to a froth.
19-02-2009, 04:13 AM #6
Hi Guys
I am a new member.look forward to joining in on some of the technical queries. Dan
09-03-2009, 04:31 AM #7
Can anybody explain me how Aspera oil cooler compressor NE2130Z works. Thanks
09-03-2009, 07:08 PM #8
Welcome to the forum.
The compressor works the same as all compressors of this type. Electrical power is used to spin a motor inside the casing which in turn uses pistons to suck in and compress refrigerant gas.
Technical details of the compressor are available here, a 1.73MB pdf file.
http://www.embraco.com.br/portugue/p..._pdf/03031.pdfBrian - Newton Abbot, Devon, UK
Superheat and Subcooling
By Chunk in forum FundamentalsReplies: 42Last Post: 15-01-2011, 01:24 AM -
Liquid charging through the suction side
By deu58 in forum FundamentalsReplies: 13Last Post: 02-07-2010, 05:23 AM -
Charging liquid through suction line?
By SloFuse in forum Trouble ShootingReplies: 15Last Post: 20-06-2010, 09:26 PM -
Charging with Liquid or Gas? (A Worthwhile Tip)
By Grizzly in forum FundamentalsReplies: 5Last Post: 07-09-2008, 10:39 PM