Multi-Hertz compressor
Our company is starting to supply our refrigerated units with 50hz compressors. Is there a compressor that has the ability to switch from 60hz to 50hz and vice versa or is there an adapter?
-
18-02-2009, 12:20 PM #2
Re: Multi-Hertz compressor
It depends on the voltage. A 60Hz, 460V compressor should run happily on 380-400V 50Hz. 1-phase compressors is probably harder to make dual Hz versions of.
-
18-02-2009, 09:23 PM #3
Re: Multi-Hertz compressor
As long as v/f is constant, no problem for the motor.
-
18-02-2009, 11:05 PM #4
Re: Multi-Hertz compressor
We typically use 220v/60hz and 120v/60hz compressors.