    Multi-Hertz compressor



    Our company is starting to supply our refrigerated units with 50hz compressors. Is there a compressor that has the ability to switch from 60hz to 50hz and vice versa or is there an adapter?



  2. #2
    Join Date
    Feb 2008
    Location
    Norway
    Age
    57
    Posts
    446
    Rep Power
    17

    Re: Multi-Hertz compressor

    It depends on the voltage. A 60Hz, 460V compressor should run happily on 380-400V 50Hz. 1-phase compressors is probably harder to make dual Hz versions of.

  3. #3
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    52
    Posts
    2,549
    Rep Power
    24

    Re: Multi-Hertz compressor

    As long as v/f is constant, no problem for the motor.

  4. #4
    captainleaky's Avatar
    captainleaky Guest

    Re: Multi-Hertz compressor

    We typically use 220v/60hz and 120v/60hz compressors.

Similar Threads

  1. LG heat pump problem
    By back2space in forum Heat Pumps
    Replies: 132
    Last Post: 01-02-2009, 11:23 PM
  2. Help with multi compressor pack systems!!!!
    By dez in forum Chit Chat & Service Stories
    Replies: 1
    Last Post: 27-11-2008, 01:09 AM
  3. SL/SB-400 Pump Down Procedures
    By absolute-zero in forum Transport
    Replies: 1
    Last Post: 29-01-2008, 09:27 PM
  4. RHOSS multi unit compressor dead
    By cool#9 in forum Air Conditioning
    Replies: 4
    Last Post: 15-06-2007, 09:19 PM
  5. Mitsi City Multi Compressor Death
    By aeb200 in forum Air Conditioning
    Replies: 4
    Last Post: 16-11-2005, 09:10 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •