18-02-2009, 03:29 AM #1
Manitowoc BY139N
Hey Guys! I'm having a problem Manitowoc Ice Machince BY139N. I have been working on this for a couple weeks and it started off with it not dropping the ice during the harvest cycles. I have a dual evap coils and the right side will drop but the left side won't. It will just keep building up and then shut down. It will drop when it is down but the ice is thick. I am running out of ideas of why it isn't dropping any help would be greatly
-
18-02-2009, 07:58 AM #2
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,151
- Blog Entries
- 6
- Rep Power
- 36
Re: Manitowoc BY139N
Check that solenoid of Hot gas valve for that evaporator is energized 45 seconds after harvest start, and that hot gas flows to evaporator by checking temperature of pipe after valve.
If valve is energized and hold magnetically (check with flat screwdriver at piston of valve) and pipe is not hot before and after valve than valve is faulty. If you don't have energized valve than solenoid or control circuit is faulty. Check that by measuring solenoid voltage! If voltage is present and OK, than solenoid is faulty. If not, than control circuit is faulty.
Last edited by nike123; 18-02-2009 at 08:15 AM.
-
18-02-2009, 08:54 PM #3
Re: Manitowoc BY139N
Thanks for the detail explanation. I'll go ahead and check all that. Thanks again
Similar Threads
-
Manitowoc Ice machine taking too long to harvest..
By nyTroX in forum Trouble ShootingReplies: 26Last Post: 08-05-2011, 09:39 PM -
Manitowoc qy600 compressor refit
By TEMP DOC in forum Trouble ShootingReplies: 4Last Post: 20-11-2008, 03:02 AM -
help with manitowoc ice machine
By edwards91 in forum Trouble ShootingReplies: 3Last Post: 28-07-2008, 04:01 AM -
Manitowoc remote condenser install
By hysiderafter in forum CommercialReplies: 0Last Post: 22-07-2008, 06:43 PM -
manitowoc ice machine harvest cycle
By flyboy3b in forum Trouble ShootingReplies: 9Last Post: 26-05-2008, 06:51 AM