    Question Back pressure regulators : 3PM50



    Sir,
    I would like to use the PM1-40 OR PM1-50 OR ( PM3-40/PM3-50) valve for the following WATER CHILLING APPLICATION @ 1 DEG C OUT ,

    1 the capacity of the plant is 45TR @ Nh3 gas, evaporation (sst) suction temp (-4 degC) , condensing (sdt) temp 38 degC,
    2.Application is chilled clear water: in temp to chiller is 5 deg c & out from chiller is 1deg. Also note that the flooded chiller used in this application is welded cassettes heat exchanger WPHE.

    We would like to maintain the constant evporative pressure (& hence the temp) in the WPHE to avoid the freezing of clear water in the channels when it comes out from the WPHE

    Pl suggest which pilot operated valve we should use with PM-1-40 ? ( CVP/CVPP/CVT/CVQ/CVC ?)


    Can you help me ?
    vinodvlimaye (india)



  2. #2
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    53
    Posts
    2,549
    Rep Power
    24

    Re: Back pressure regulators : 3PM50

    What brand is that valve?

  3. #3
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: Back pressure regulators : 3PM50

    1°C chilled water is approaching an area where you run the risk of operational problems. A -4°C evaporating temperature adds to the potential problem.

    Even with a back pressure regulator that holds a constant evaporating pressure.

    This is really, really difficult to accomplish and work long term (successfully).
    If all else fails, ask for help.


  4. #4
    Join Date
    Feb 2008
    Location
    Norway
    Age
    57
    Posts
    446
    Rep Power
    17

    Re: Back pressure regulators : 3PM50

    I suppose some sort of flooded evaporator is the best solution in this case. And a generously sized evaporator having the necessary capasity at a relatively high evaporation temp like -1°C.

  5. #5
    Join Date
    Dec 2007
    Location
    australia
    Posts
    3,357
    Rep Power
    39

    Re: Back pressure regulators : 3PM50

    Its a danfoss valve and you could use a PM3 with a CVQ and EVM solonoid in series . Measuring /controlling outlet water temp to modulate valve .
    A water flow switch can be installed as back up .
    If water flow switch and / or water temp to low , turn EVM off to stop refrigeration to prevent freeze up .
    Compressor could also be shut down if dedicated to that system only .
    Check with danfoss rep .

  6. #6
    Join Date
    Sep 2008
    Location
    India
    Age
    39
    Posts
    24
    Rep Power
    0

    Re: Back pressure regulators : 3PM50

    Hi... Vinod...
    1. For Back Pressure regulating valve Model PM1-40/ PM1-50, the pilot valve is CVP(LP) should be used and it is purely mechanical valve.
    2. For Back Pressure regulating valve Model PM3-40/ PM3-50, the pilot valve is CVQ with EVM coil should be used and it is electrical operated valve.
    3. PM1 valve is cheeper than PM3 valve

Similar Threads

  1. Replies: 27
    Last Post: 27-10-2006, 03:19 AM
  2. Short Cycling blues & low pressure control switch
    By mccoolair@yahoo in forum Supermarket Refrigeration
    Replies: 14
    Last Post: 09-04-2006, 09:28 PM
  3. screw compressor
    By vinod in forum Trouble Shooting
    Replies: 9
    Last Post: 17-12-2005, 01:46 AM
  4. Compressor back pressure rating
    By Cary in forum Fundamentals
    Replies: 9
    Last Post: 05-12-2004, 08:42 AM
  5. Low back pressure compressor application
    By Abe in forum Technical Discussions
    Replies: 5
    Last Post: 31-07-2001, 11:43 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •