    Corrosion of steam condensate line



    Hi members,

    In absorption chiller, steam condensing temp. in
    generator becomes negative and sometimes very low at partial load operation. Matter is how to remove it smoothly because the receiver tank pressure will peak out at the equivalent pressure even if you use a vacuum pump. Trane/York IOM recommend to install a vacuum breaker in the generator steam side. It looks very simple and low-cost solution.
    My concern is corrosion of generator and condensate piping of the chiller because steam condensate is possible to cause corrosion w/o much air(oxygen) and it must be worse by this vacuum breaking.
    Does anybody have an experience of the vacuum breaking and corrosion ?



  2. #2
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,357
    Rep Power
    37

    Re: Corrosion of steam condensate line

    Beppo . You have a very big problem with corrosion in steel pipes, if boiler generated steam the water treatment is not working, if geothermal the strubbers are not working. You need to replace all pipework and sort out treatment and or scrubbers. Not and easy exercise and very expensive repair.
    magoo

  3. #3
    Join Date
    Feb 2009
    Location
    Japan
    Posts
    5
    Rep Power
    0

    Re: Corrosion of steam condensate line

    Magoo, Thank you for the suggestion. I understand how the water treatment is important for boiler steam.

  4. #4
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Corrosion of steam condensate line

    Quote Originally Posted by ubs2009 View Post
    back up!!!!!!!
    Thanks man!
    Your answer is very helpful and informative. When you catch some more time, please, enlighten us with more of your wisdom.

Similar Threads

  1. Superheat and Subcooling
    By Chunk in forum Fundamentals
    Replies: 42
    Last Post: 15-01-2011, 01:24 AM
  2. Coolpack help
    By marc5180 in forum Fundamentals
    Replies: 42
    Last Post: 31-01-2009, 10:28 PM
  3. Low Pressure Cut-off switch on Liquid line
    By Vishnukurup in forum Air Conditioning
    Replies: 14
    Last Post: 03-12-2008, 09:34 AM
  4. Corrosion.
    By romaurie in forum Industrial
    Replies: 4
    Last Post: 27-11-2005, 10:57 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •