20-04-2004, 09:44 PM #1
superheat help
Hey all, my question is this... what is the procedure necessary to measure the amount of superheat supplied at the sensing phial by the an internally equalised tev ?
does that sound more confusing than it is, or is lack of sleep jus making me dumber ?
my attempted answer is to check the evap temp via gauges against the temp at the phial,noting a diff of approx 6°c (in a frozen food display unit)
-
20-04-2004, 11:55 PM #2
Re: superheat help
Originally Posted by Krups
Originally Posted by KrupsProf Sporlan
-
21-04-2004, 12:03 AM #3
Re: superheat help
thanks prof, are u really a prof ?
and what is dew point temperature ? and why the conversion to this ? iv never come across that ? unless its also known under another term..
-
21-04-2004, 02:48 PM #4
Re: superheat help
hi krups,
I do it, using two probe thermometer.
one sensor is connected at the TEV outlet - T1
the second, at the outlet of the evaporator - T2
adjust the superheat when system is properly charged.
its basicly the same as the Prof says but you dont always get a schreder valve at the evaporator outlet.
chemi
-
22-04-2004, 12:15 AM #5
Re: superheat help
Originally Posted by Krups
Originally Posted by Krups
Originally Posted by chemi-coolProf Sporlan
-
28-04-2004, 11:23 AM #6
Re: superheat help
thnx people, this has been very useful
Similar Threads
-
TXV Superheat
By Gary in forum Trouble ShootingReplies: 15Last Post: 24-04-2011, 02:51 PM -
Carrier 23xl chiller-Low discharge superheat alarms
By Bradysmill in forum Trouble ShootingReplies: 7Last Post: 25-04-2010, 07:43 PM -
TEV superheat setting and low temperatures
By DaBit in forum FundamentalsReplies: 11Last Post: 01-03-2010, 02:11 AM -
Superheat debate
By zolar1 in forum Technical DiscussionsReplies: 5Last Post: 08-02-2008, 09:57 PM -
Superheat
By shogun7 in forum FundamentalsReplies: 24Last Post: 23-08-2004, 05:54 PM