    York Recip NH3 Compressor Info



    I am looking for anyone with information regarding the required GPM of water required to cool the following York ammonia compressors operating @ 20F and 95F:
    York A-3069
    York A-3089
    York A-589

    York manual engineering manual would also be helpful.

    Thanks,

    CIR391



  2. #2
    Join Date
    May 2006
    Location
    India
    Age
    74
    Posts
    399
    Rep Power
    18

    Re: York Recip NH3 Compressor Info

    Water circulation rate for jackets of NH3 compressor :
    a) water qty : 1 gpm / 25 TR
    b) inlet / outlet temp difference should be : 15 deg C / 29 deg F
    C) COOLING INLET WATER TEMP NEVER TO BE LESS THAN CONDENSING TEMP ; 95 DEG F IN YOUR CASE.
    d) swich off water supply to jackets when compressor is not operating .
    More info in W.F.Stoecker Industrial Refrigeration Handbook ( page 120)