    Flash Gas



    Does any one have an idea on how long it takes the liquid to turn into gas once the pressure is dropped.

    For instance - through a TXV. Does the gas form instantaneously or is there a delay, a delay of 10ms or 300ms would make a huge differance.

    Another example - if a liquid line ruptures does it spray liquid onto the floor which then evaporates or does it come out of the leak as a all gas?

    For a pure refrigerant it may be quick but with oil added to the mixture the oil may hold back the flash off for some time?

    Any ideas or referances?

    Thanks

    Chef



  2. #2
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,175
    Blog Entries
    6
    Rep Power
    36

    Re: Flash Gas

    Quote Originally Posted by Chef View Post

    Another example - if a liquid line ruptures does it spray liquid onto the floor which then evaporates or does it come out of the leak as a all gas?

    This is easy to simulate. Hook manifold hose on gas cylinder and release liquid refrigerant in hose. At exit you will see drops of liquid refrigerant as well as gas. So, it has both phases and it is obvious that liquid is not momentary evaporated.

    Then again, when we search for definition of flash gas we get this:
    The gas resulting from the instantaneous evaporation of refrigerant in a pressure-reducing device to cool the refrigerant to the evaporating temperature obtaining at the reduced pressure.
    This calculator could be handy!
    Last edited by nike123; 11-02-2009 at 08:59 AM.

  3. #3
    Join Date
    Jun 2007
    Location
    At sea
    Posts
    367
    Rep Power
    17

    Re: Flash Gas

    Quote Originally Posted by nike123 View Post
    This is easy to simulate. Hook manifold hose on gas cylinder and release liquid refrigerant in hose. At exit you will see drops of liquid refrigerant as well as gas. So, it has both phases and it is obvious that liquid is not momentary evaporated.


    This calculator could be handy!
    Thanks Nike: I can remember when filling a gas lighter with butane the gas/liquid would spray out if the seal was a bit off. The butane took some some time to evaporate so I get the idea. Not sure if I want to squirt refrigerant onto the floor just yet but the mental image is good.

    I tried the calculator you linked to and thanks for that but as it uses EES in the two phase region it sometimes makes mistakes (always actually) and I get 42% liquid and 99.3% gas so it seems to be a little (lot) off.

    If the liquid does take some time to evaporate as is now expected, per your thought experiment with the gas bottle, it means that liquid may be squirted out of a TXV valve directly into the evaporator a bit like a fire hose.

    That changes a whole lot of assumptions of what is happening. What if the entrance to the evaporator is 90% liquid instead of the average 70% normally assumed? Velocities are off, heat absorption changes.

    Somehow I need to get a time constant for liquid to gas.

    Chef

  4. #4
    TRASH101's Avatar
    TRASH101 is offline Veteran Poster I am starting to push the Mods: of RE
    Join Date
    Mar 2007
    Location
    england
    Posts
    397
    Rep Power
    18

    Re: Flash Gas

    Good day to you Chef

    To my way of thinking the rate vaporization would depend almost entirely on the pressure drop (i.e. velocity) at the aperture/rupture and localised energy available. I would envisage that a cone of liquid would be existant at the aperture maintained by the head of liquid behind in conjunction with the cooling effect of the instantaneous evaporation surrounding the cone. I also believe that a proportion of the vapor will re-condense (if localised energy sources allow). The interesting point is the oil, as it is not an emulsion (hopefully) it is only suspended and must make some physical difference to the rate of evaporation.

    Thats what I think happens. I might read up about this if I get time.
    Quidvis Recte Factum Quamvis Humile Praeclarum.

    Latine dictum, sit altum videtur.

    Si hoc comprehendere potes, gratias age magistro Latinae.

  5. #5
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,175
    Blog Entries
    6
    Rep Power
    36

    Re: Flash Gas

    Quote Originally Posted by Chef View Post
    T

    I tried the calculator you linked to and thanks for that but as it uses EES in the two phase region it sometimes makes mistakes (always actually) and I get 42% liquid and 99.3% gas so it seems to be a little (lot) off.
    I dont see where in software you found % Liquid and % Gas.

    I see only % volume of flash gas and % mas of flash gas.

    In your case that probably mean
    42% of mass of flash gas and 58% mass of liquid refrigerant
    and in same time
    99,3% volume of flash gas and 0,7% volume of liquid refrigerant
    and that sound to me perfectly OK!



  6. #6
    Join Date
    Jun 2007
    Location
    At sea
    Posts
    367
    Rep Power
    17

    Re: Flash Gas

    Hi Nike

    I did not mean to get into a discussion on the program and it should probably have its own thread.

    The real interest is in how long it takes for the gas to flash off.

    However I greatly appreciate all the effort you put in to post the diagrams and so send in your reply. Its so time consuming to post a picture.




    As you can see the % volume is 100% but the mass is only 53%.
    Something is wrong here. It does not really compute.

    I can explain why this happens in EES if you wish and it may be an intersting topic but its not what I seek at the moment.

    Your initial post about the delay of vapourisation is thought provoking but how do we quantify the time it takes. I think it will make a lot of differance to both condensation processes and evaporation processes and might have quite an impact on how we calculate things.

    I am trying to see what 100ms and 500ms differance makes on the performance of a system but its proving difficult as I have nothing to go on.

    Chef

  7. #7
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,175
    Blog Entries
    6
    Rep Power
    36

    Re: Flash Gas

    You are probably right regarding that software maybe need separate thread and I started new thread about that.

    To me, it takes about 1-2min. (depending on size of picture and if I add notes to picture).
    Snagit software and Flickr pictures server.
    Last edited by nike123; 11-02-2009 at 02:38 PM.

Similar Threads

  1. flash gas
    By bandit in forum Fundamentals
    Replies: 13
    Last Post: 19-09-2010, 06:21 PM
  2. shining fault codes
    By al in forum Air Conditioning
    Replies: 3
    Last Post: 17-07-2010, 08:34 AM
  3. How to check Flash gas?
    By Uni in forum Fundamentals
    Replies: 23
    Last Post: 22-01-2009, 08:43 PM
  4. carrier 7 flash code???
    By coolflow in forum Air Conditioning
    Replies: 2
    Last Post: 10-07-2008, 10:27 PM
  5. Flash Gas
    By packie81 in forum NH3
    Replies: 1
    Last Post: 20-12-2007, 02:31 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •