    ua daikin fault



    hi chaps, i have a problem with a twin daikin system, one of my collages has replaced an outdoor pcb on a ry71gz7w1 3ph r407 outdoor now the system has faulted up a ua code (too many fan coils) i have set it up for a twin system with the controller setting 11, 0.02 i dont have any info on the outdoor board but have been told all the bit switches were set the same as the old one. any idears? tyred to ring daikin at 4.45pm uk time but got no answer

    sorry the indoor units are fhyc35kzv1 x2



  2. #2
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: ua daikin fault

    Try the SKy Air manual from the Daikin site.

    You need file ESIE99-01 Series G
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  3. #3
    Join Date
    Mar 2006
    Location
    newcastle upon tyne
    Posts
    51
    Rep Power
    19

    Re: ua daikin fault

    thanks brian

  4. #4
    Join Date
    Sep 2006
    Location
    italy
    Age
    53
    Posts
    93
    Rep Power
    18

    Re: ua daikin fault

    Is happened before to receive an spare part PCB that has an software for another type of refrigerant. In that case you will have the same error UA. For Sky unit, from the outdoor dip-switches you don`t have the possibility to set the type of refrigerant (like for VRV outdoor PCB).

  5. #5
    Join Date
    Mar 2006
    Location
    newcastle upon tyne
    Posts
    51
    Rep Power
    19

    Re: ua daikin fault

    been back today setup code 11 and 21 on the controller to twin setting, disconnected a condensate pump from indoor connections 1 and 3 (l and n) on marster, system running ok reconnected pump still ok, i just dont know? as far as i can tell the outdoor pcb is pre set for 407 and the only bit switches are for the defrost and emergency run but i stand to be corrected, thanks for help people

  6. #6
    Join Date
    Nov 2007
    Location
    London
    Posts
    461
    Rep Power
    17

    Re: ua daikin fault

    the reason this is happening is because you may have a link between the two fan coils on p1 and p2 and this must be removed as there should only be the p1 and p2 connected on the master unit

Similar Threads

  1. Daikin r407c 2 pipe vrv ja fault code any offers?
    By Contactor in forum Air Conditioning
    Replies: 11
    Last Post: 28-07-2009, 01:26 AM
  2. Daikin fault codes
    By Markie in forum Air Conditioning
    Replies: 16
    Last Post: 13-01-2009, 01:58 AM
  3. Daikin Cassette Fault
    By symon22 in forum Air Conditioning
    Replies: 5
    Last Post: 23-05-2008, 06:19 PM
  4. UA Daikin Fault Code
    By jedi in forum Air Conditioning
    Replies: 2
    Last Post: 23-07-2007, 01:44 PM
  5. u4 fault on a Daikin inverter
    By phil17 in forum Air Conditioning
    Replies: 39
    Last Post: 05-02-2007, 02:41 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •