Best blend discovered so far
See the attachment and decide yourself in light of my research paper that R417A(isceon 59) is best low temp refrigerant and direct replacement of R22
and
Dudes no oil change is necessary
Our nose is our personal air-conditioning system: it warms cold air, cools hot air and filters impurities
-
19-04-2004, 09:57 AM #2
Re: Best blend discovered so far
First time I'm hearing about this.
Will do some search.
Good tip Abbasi.
PeterLast edited by Peter_1; 19-04-2004 at 10:06 AM.
-
19-04-2004, 10:08 AM #3
Re: Best blend discovered so far
Originally Posted by Peter_1
Kind Regards. Andy.
-
19-04-2004, 10:14 AM #4
Re: Best blend discovered so far
Andy,
You're right
http://www.isceon-refrigerants.co.uk...9-product.html
Diagrams are the same.
Will anyway have a closer look at it.
Have a nice day.
Peter
-
27-04-2004, 05:07 AM #5
Re: Best blend discovered so far
Originally Posted by Andy
please can u give me insight as what iwud happen (practically)
if we use R417A in compressor of R22
as said no system changes are required how much is this true
and y dont
comp manufacurers not mention R417A in catalogues with R407C the former being better 1
and same priceOur nose is our personal air-conditioning system: it warms cold air, cools hot air and filters impurities
-
27-04-2004, 12:03 PM #6
Re: Best blend discovered so far
Hi abbasi
the big differance with R407c would be the oil Ester oil is required, but with Isceon 59 no oil changes (apart from normal service changes) is required.
Kind Regards. Andy.
-
28-04-2004, 01:03 AM #7
Re: Best blend discovered so far
R-417A dew point pressures run below both R-22 and R-407C. At 20°F, R-417A dew point pressure is about 9 psi below R-22 compared to about 5 psi for R-407C. It may become a bit problematic to use a standard R-22 TEV with R-417A as the lower pressures will tend the TEV to overfeed. But R-417A has a lower net refrigerating effect than R-22 which also effectively reduces TEV capacity. As a result, care must be exercised when converting R-22 systems with TEVs to R-417A.
BTW, the Prof has pondered the Rhodia marketing considerations calling their new line of refrigerant blends the "9 series", i.e., ISCEON 29, 39, 49, 59, 69, 79, 89. What is the significance of the number 9? It is a perfect square. The Hebrews referred to 9 as the symbol of immutable truth. The Ennead is a 9 pointed star, and it once was a sacred symbol...
The Prof would have opted for the "8 series" however... It would seem much more prosperous. It is the basis of a monetary system. "Pieces of Eight" and "yo ho ho and a bottle of rum". Ok, the Prof has been drinking a wee heavy and needs to rest.Prof Sporlan
-
28-04-2004, 08:31 AM #8
Re: Best blend discovered so far
Originally Posted by Prof Sporlan
I have little experience with Isceon 59 but I know the net refrigeration effect goes down , but the C.O.P goes up. Isceon 69L is the one I have used the most, it is a very good gas, but gives you a lot more refrigerating effect, with an increase in C.O.P, on 69L condensers become too small, design pressures have to be looked at and drive motors can run at their limits but if it's extra capacity you need without chaging the system, on low temperature R69L is the one.
I suppose one good this with R59 is the fact that more condensing surface becomes available and you never have that problem to consider
Kind Regards Andy
-
28-04-2004, 08:37 PM #9
Re: Best blend discovered so far
I've heard that 59 has oil return problems and the oil tends to foam a lot - is this true - has anyone else heard this?
Only ever used 49 myself as a replacement for R12 in a chill room as we don't tend to work on low temp installations.
Similar Threads
-
Natural Refrigerants
By baker in forum RefrigerantsReplies: 7Last Post: 26-10-2010, 05:28 PM -
what is the best blend for low temp
By tony_rich in forum RefrigerantsReplies: 87Last Post: 05-08-2006, 08:29 AM -
About gas blend properties (how can high pressure components condense?)
By DaBit in forum FundamentalsReplies: 17Last Post: 11-02-2004, 02:23 AM