    temperzone lp faults



    hi there guys, hope all is well with ya all, im want to ask if any body may have had some lp issues with temperzone split ducteds,,, i curently have 3 in the one building a rather new building, they are all coming up with low pressure faults, all units run for 5 or so mins and off for 3 or so, all units are running simular pressures and temps, liq line 215psi (1500kpa) and 40 deg cel at outdoor unit suct line was 70 psi (480kpa) and 25 deg cel,,, model of units are OSA126R, these unit hav option for lp switch or bypass,, these ones are bypassed, no lp switch, tech support advised the lp fault would be initiated by suction line sensor?? they also advised to get superheat to approx 4-6k,, ok so i have 70psi indicating 4-6 deg cel in evap on R22, (pressure taken at service valve at outdoor) and i have 25 deg cel on suction line at outdoor unit giving me 19-21k sup ht?? tech suppot wants approx 10deg cel at this pressure,, they suggested short of refrigerant???? i think pressures are a bit high??? i thought around 60 psi suct was good, the ambient of the day these measurements taken was around 26-27 deg, and pipe runs were approx 12-14 meteres, there is absolutly no way in heaven you can get good access to any of the fan coil units its a crazy install if ya ask me but this could be the norm??? take it easy guys dont work too hard



  2. #2
    Join Date
    Jul 2007
    Location
    Australia
    Age
    50
    Posts
    1,845
    Rep Power
    20

    Re: temperzone lp faults

    Yep, the sense the suction line temp, not the pressure. The thermistor is normally near the reversing valve.
    So if the suction line temp is a bit high, or the thermistor is buggered, you'll get "LP" faults.
    You are gettin "LP" faults because, as you said, the suction line is 25C, so superheat is to high.

  3. #3
    Join Date
    Feb 2007
    Location
    Australia
    Age
    70
    Posts
    15
    Rep Power
    0

    Re: temperzone lp faults

    The suction temperture sensor should be around 10K. I went to the trouble of adjusting the TX on the ISD300Q to find the LP problem did't go away. The sensor was only 1K and didn't show as a sensor fault.

  4. #4
    Join Date
    Nov 2008
    Location
    NELSON BAY AUST
    Age
    43
    Posts
    48
    Rep Power
    0

    Re: temperzone lp faults

    thanks guys, i think i need to play with refrigerant levels, just wanting to ask if yas dont mind, in your experience is there a rough idea on the suction pressure im looking for??? i know 4-6 k super heat is required but i have suction of 70psi (4-6 deg cel coil temp) by adding refrigerant would i not then raise suct pressure and coil temp and make unit useless anyway?? but on the other hand, do i add more to allow more liquid in evap so then it refrigerates down suction line thus allowing me to reduce suction line temp to acheive 4-6 k superheat, im confussed

  5. #5
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: temperzone lp faults

    Quote Originally Posted by TECH TIM View Post
    thanks guys, i think i need to play with refrigerant levels, just wanting to ask if yas dont mind, in your experience is there a rough idea on the suction pressure im looking for??? i know 4-6 k super heat is required but i have suction of 70psi (4-6 deg cel coil temp) by adding refrigerant would i not then raise suct pressure and coil temp and make unit useless anyway?? but on the other hand, do i add more to allow more liquid in evap so then it refrigerates down suction line thus allowing me to reduce suction line temp to acheive 4-6 k superheat, im confussed
    Do not play with refrigerant levels. Evacuate, evaluate, fix leak if short of refrigerant, then recharge correct amount by weight.

  6. #6
    Join Date
    Jul 2007
    Location
    Australia
    Age
    50
    Posts
    1,845
    Rep Power
    20

    Re: temperzone lp faults

    Best bet is not to play with them and guess or be concerned with pressure. They are not large systems so you are better to reclaim, pressure test, evac and recharge after checking no resctrictions on the piping.
    I'm saying that because you have relitively new systems, and if I understand right, all 3 have the same fault?
    Possibly bad installation could be the cause then, so I wouldn't be topping up, I'd be starting from scratch.
    They could be just undercharged at the time of install, but there could be air in the system, leaks on the joins etc.

  7. #7
    Join Date
    Nov 2008
    Location
    NELSON BAY AUST
    Age
    43
    Posts
    48
    Rep Power
    0

    Re: temperzone lp faults

    thanks paul i was contamplaiting that now im going too do it cheers mate

Similar Threads

  1. Temperzone. Good/Bad?
    By MadMax in forum Commercial
    Replies: 11
    Last Post: 06-02-2010, 12:30 AM
  2. Information on faults etc HELP
    By maxcool in forum Refrigeration Books
    Replies: 4
    Last Post: 17-12-2008, 08:40 PM
  3. Daikin faults
    By IanH74 in forum Air Conditioning
    Replies: 5
    Last Post: 26-05-2008, 11:53 PM
  4. Earth faults
    By reggie in forum Technical Speculations
    Replies: 17
    Last Post: 28-01-2006, 06:22 PM
  5. Mitsu faults
    By Abe in forum Air Conditioning
    Replies: 2
    Last Post: 31-03-2003, 07:30 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •