10-02-2009, 02:00 AM #1
Back pressure valves
Hi Guys,
been having some fun a new A4AS back pressure valve on a PHE for chilled water, it seems to not want to open and modulate or it opens and wont close off on the set spring.
Seems the only ay to get it operating to some degree is to throttle the down stream suction valve and the liquid feed valve, any advice appreciated
the suction is into the HP side of a two stage system running about 2 bar
-
12-02-2009, 11:31 AM #2
Re: Back pressure valves
I would guess that you have a small piece of crud stuck in the valve. It doesn't take but just a tiny piece of pipe scale or dirt inside these valves to make them fail. I would order a valve kit and simply rebuild the valve. It is pretty easy to do.
Is it possible that you have the manual opening stem on the bottom of the valve opened? That would prevent the valve from working.
You can find the info on that valve here on line # 23-06; http://www.parker.com/portal/site/PA...vision#resultsLast edited by Oregon Jim; 12-02-2009 at 11:41 AM. Reason: add more info
-
16-02-2009, 07:26 AM #3
Re: Back pressure valves
Thanks mate, the service manual off that link has it all
cheers
-
17-02-2009, 05:44 AM #4
Similar Threads
-
Compressor loading, cooling, and range of operation.
By Air duster in forum FundamentalsReplies: 10Last Post: 02-04-2008, 08:39 AM -
Screw compressor system losing oil differential pressure
By orm in forum Trouble ShootingReplies: 27Last Post: 27-10-2006, 03:19 AM -
back pressure valve in chiller
By vinod in forum Air ConditioningReplies: 2Last Post: 12-06-2006, 06:29 PM -
Building a wine cabinet
By Rory in forum Technical DiscussionsReplies: 38Last Post: 13-07-2004, 08:28 PM -
Low back pressure compressor application
By Abe in forum Technical DiscussionsReplies: 5Last Post: 31-07-2001, 11:43 PM