    Back pressure valves



    Hi Guys,
    been having some fun a new A4AS back pressure valve on a PHE for chilled water, it seems to not want to open and modulate or it opens and wont close off on the set spring.
    Seems the only ay to get it operating to some degree is to throttle the down stream suction valve and the liquid feed valve, any advice appreciated
    the suction is into the HP side of a two stage system running about 2 bar



  2. #2
    Join Date
    Mar 2008
    Location
    Dallas, Oregon
    Age
    72
    Posts
    51
    Rep Power
    17

    Re: Back pressure valves

    I would guess that you have a small piece of crud stuck in the valve. It doesn't take but just a tiny piece of pipe scale or dirt inside these valves to make them fail. I would order a valve kit and simply rebuild the valve. It is pretty easy to do.

    Is it possible that you have the manual opening stem on the bottom of the valve opened? That would prevent the valve from working.

    You can find the info on that valve here on line # 23-06; http://www.parker.com/portal/site/PA...vision#results
    Last edited by Oregon Jim; 12-02-2009 at 11:41 AM. Reason: add more info

  3. #3
    Join Date
    Feb 2008
    Location
    New Zealand
    Posts
    12
    Rep Power
    0

    Re: Back pressure valves

    Thanks mate, the service manual off that link has it all
    cheers

  4. #4
    Join Date
    Sep 2008
    Location
    Canada
    Posts
    811
    Rep Power
    18

    Re: Back pressure valves

    Quote Originally Posted by Loafa View Post
    Hi Guys,
    been having some fun a new A4AS back pressure valve on a PHE for chilled water, it seems to not want to open and modulate or it opens and wont close off on the set spring.
    Seems the only ay to get it operating to some degree is to throttle the down stream suction valve and the liquid feed valve, any advice appreciated
    the suction is into the HP side of a two stage system running about 2 bar
    Probably, your valve is oversized. Oversized valves have unstable operation. Throttle upstream and downstream of this valve.

Similar Threads

  1. Compressor loading, cooling, and range of operation.
    By Air duster in forum Fundamentals
    Replies: 10
    Last Post: 02-04-2008, 08:39 AM
  2. Replies: 27
    Last Post: 27-10-2006, 03:19 AM
  3. back pressure valve in chiller
    By vinod in forum Air Conditioning
    Replies: 2
    Last Post: 12-06-2006, 06:29 PM
  4. Building a wine cabinet
    By Rory in forum Technical Discussions
    Replies: 38
    Last Post: 13-07-2004, 08:28 PM
  5. Low back pressure compressor application
    By Abe in forum Technical Discussions
    Replies: 5
    Last Post: 31-07-2001, 11:43 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •