    Does anyone know how you are able to determine the type of refrigerant that is already inside the system? Sometimes the type of refrigerant that is actually inside the system is not the actual type that is specified on the unit's tag. Is there any way to tell what has actually been used in the system?

    Any advice is appreciated. Thanks.



  2. #2
    Join Date
    Mar 2007
    Location
    Warwickshire UK
    Posts
    723
    Rep Power
    21

    Re: How do you determine type of refrigerant in the system?

    Try taking the standing pressure of the refrigerant in the system & ambient temperature.
    Look on a refrigerant comparitor to see which refrigerant has pressure which is a match for the temp.
    Provided the system still has some liquid refrigerant this basic test should give first indication.

  3. #3
    Join Date
    Nov 2006
    Location
    UK
    Age
    50
    Posts
    708
    Rep Power
    23

    Re: How do you determine type of refrigerant in the system?

    look on TEV if fitted ,look at compressor lable for ref type or drier ,if its worth it get a sample analized

  4. #4
    Join Date
    Feb 2007
    Location
    UK
    Age
    58
    Posts
    158
    Rep Power
    18

    Re: How do you determine type of refrigerant in the system?

    Quote Originally Posted by Quality View Post
    look on TEV if fitted ,look at compressor lable for ref type or drier
    I see you've never worked on a "greencool" chiller.

    Every component says R22 - they contain PROPANE.



    Keep clicking yer pen top

  5. #5
    Join Date
    Nov 2006
    Location
    UK
    Age
    50
    Posts
    708
    Rep Power
    23

    Re: How do you determine type of refrigerant in the system?

    i have not I take the hint

  6. #6
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: How do you determine type of refrigerant in the system?

    The only way to be sure is to get the refrigerant analysed or use a refractometer.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  7. #7
    Join Date
    Nov 2006
    Location
    UK
    Age
    50
    Posts
    708
    Rep Power
    23

    Re: How do you determine type of refrigerant in the system?

    Quote Originally Posted by Brian_UK View Post
    The only way to be sure is to get the refrigerant analysed or use a refractometer.
    ok another sarcastic remark

  8. #8
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: How do you determine type of refrigerant in the system?

    Quote Originally Posted by Quality View Post
    ok another sarcastic remark
    Not really, but if you read the OP you will realise that your answer does not relate to it.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  9. #9
    Join Date
    Nov 2006
    Location
    UK
    Age
    50
    Posts
    708
    Rep Power
    23

    Re: How do you determine type of refrigerant in the system?

    words eaten or something like that ,oil and what has been

  10. #10
    Join Date
    Oct 2006
    Location
    England
    Posts
    1,843
    Rep Power
    21

    Re: How do you determine type of refrigerant in the system?

    .

    Just check all the empty cylinders that will be dumped in the plantroom.

    taz.

    .

  11. #11
    Join Date
    Oct 2007
    Location
    NZ
    Posts
    85
    Rep Power
    17

    Re: How do you determine type of refrigerant in the system?

    Quote Originally Posted by Plank! View Post
    I see you've never worked on a "greencool" chiller.

    Every component says R22 - they contain PROPANE.



    Keep clicking yer pen top
    Did you say test flamability???

  12. #12
    Join Date
    Jul 2008
    Location
    Singapore
    Posts
    11
    Rep Power
    0

    Re: How do you determine type of refrigerant in the system?

    Hi! I know of an analyser under the barndname TASCO which is designed to determine the refrigerant compositions. The machine can even identify most HFC and even CFCs.

    Hope it helps!

    Regards
    Koh - S'pore

Similar Threads

  1. Refrigerant recovery system
    By Dns in forum Refrigerants
    Replies: 3
    Last Post: 15-04-2010, 02:38 PM
  2. Calorex Pool Heater
    By airefresco in forum Heat Pumps
    Replies: 22
    Last Post: 06-02-2009, 09:03 AM
  3. Replies: 29
    Last Post: 02-10-2008, 09:48 PM
  4. How an expansion tank works?
    By Raadster in forum Fundamentals
    Replies: 6
    Last Post: 25-07-2008, 02:25 PM
  5. inverters pulling vacuum
    By bangoman in forum Air Conditioning
    Replies: 2
    Last Post: 05-02-2008, 09:12 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •