Results 1 to 12 of 12
    tomtom's Avatar
    tomtom Guest
    How do you determine type of refrigerant in the system?
    Does anyone know how you are able to determine the type of refrigerant that is already inside the system? Sometimes the type of refrigerant that is actually inside the system is not the actual type that is specified on the unit's tag. Is there any way to tell what has actually been used in the system?
    Any advice is appreciated. Thanks.
    Mar 2007
    Warwickshire UK
    723
    Re: How do you determine type of refrigerant in the system?
    Try taking the standing pressure of the refrigerant in the system & ambient temperature.
    Look on a refrigerant comparitor to see which refrigerant has pressure which is a match for the temp.
    Provided the system still has some liquid refrigerant this basic test should give first indication.
    Nov 2006
    708
    look on TEV if fitted ,look at compressor lable for ref type or drier ,if its worth it get a sample analized
    Feb 2007
    58
    158
    Quote Originally Posted by Quality View Post
    I see you've never worked on a "greencool" chiller.
    Every component says R22 - they contain PROPANE.
    Keep clicking yer pen top
    Nov 2006
    708
    i have not I take the hint
    The only way to be sure is to get the refrigerant analysed or use a refractometer.
    Nov 2006
    708
    ok another sarcastic remark
    Not really, but if you read the OP you will realise that your answer does not relate to it.
    Nov 2006
    708
    words eaten or something like that ,oil and what has been
    Oct 2006
    1,843
    Just check all the empty cylinders that will be dumped in the plantroom.
    taz.
    NZ
    85
    Quote Originally Posted by Plank! View Post
    Did you say test flamability???
    Jul 2008
    Singapore
    11
    Hi! I know of an analyser under the barndname TASCO which is designed to determine the refrigerant compositions. The machine can even identify most HFC and even CFCs.
    Hope it helps!
    Koh - S'pore
  1. Refrigerant recovery system
    By Dns in forum Refrigerants
    Last Post: 15-04-2010, 02:38 PM
  2. Calorex Pool Heater
    By airefresco in forum Heat Pumps
    Last Post: 06-02-2009, 09:03 AM
  3. Replies: 29
    Last Post: 02-10-2008, 09:48 PM
  4. How an expansion tank works?
    By Raadster in forum Fundamentals
    Last Post: 25-07-2008, 02:25 PM
  5. inverters pulling vacuum
    By bangoman in forum Air Conditioning
    Last Post: 05-02-2008, 09:12 PM