dx alp 100 mc quay
hi
i am having a problem with this dx system which is having a flood back ,after changing the EXV still the problem is same ,the AHU cap 37000 btu.even thou the ahu is running u can still open the motor panel door without any force,is the AHU under cap or their any other problem beside this
-
09-02-2009, 08:04 PM #2
Re: dx alp 100 mc quay
Are there any duct dampers that have been closed ?
Fire dampers ?
If no suction pressure on fan then the discharge is blocked somewhere.
Resolve airflow problem before touching the refrigeration side.Brian - Newton Abbot, Devon, UK