    LP/HP Connector Lines



    I've been told that flexible lines for LP/HP cut outs doesn't work good in cold wheather conditions.

    The ID orifice (2 mm) clogs with oil and results vary with climatic conditions. Compressor sometimes goes into vacuum during pumpdown.

    Do we need bigger dia. lines (1/4") copper pipe??

    I've even seen small capillaries used with these controls (Danfoss).

    Any views???



  2. #2
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,175
    Blog Entries
    6
    Rep Power
    36

    Re: LP/HP Connector Lines

    Since thru these lines there is no flow, only difference is in time to equalization off pressure changes at other side of tube. Since oil is not solidified, eventually pressure of system will be transmitted to control.
    Bigger tube diameter means faster response at HP/LP control.

    I have installed on some equipment longer and thinner lines as dampening device in order to avoid unnecessary triggering of high pressure switch caused by pressure bursts from compressor.
    Last edited by nike123; 09-02-2009 at 10:05 AM.

  3. #3
    Join Date
    Jun 2008
    Location
    India
    Age
    56
    Posts
    64
    Rep Power
    16

    Re: LP/HP Connector Lines

    Quote Originally Posted by jwasir View Post
    I've been told that flexible lines for LP/HP cut outs doesn't work good in cold wheather conditions.

    The ID orifice (2 mm) clogs with oil and results vary with climatic conditions. Compressor sometimes goes into vacuum during pumpdown.

    Do we need bigger dia. lines (1/4") copper pipe??

    I've even seen small capillaries used with these controls (Danfoss).

    Any views???
    Having flexi capillary connection to pressure cutouts and pressure gauges is a good method for longevity of cutouts and gauges. Whenever I located the HP cutout lines away from the warm condenser air ambient - in an isoltaed instrument panel, the high pressure rerigerant condenses in the flexi lines and naturally will have some oil also with it in noticeable amount. The presence of liquid and oil in the connecting tubes of cutouts does not affect the protection in any way.
    The suction cutout pressure tapping on the suction tubing has to be from the top side of suction line. Is your LP cutout set at wrong value or faulty to let the compressor run in vacuum?

  4. #4
    Join Date
    Apr 2006
    Location
    Canada
    Age
    53
    Posts
    154
    Rep Power
    18

    Re: LP/HP Connector Lines

    The suction cutout pressure tapping on the suction tubing has to be from the top side of suction line. Is your LP cutout set at wrong value or faulty to let the compressor run in vacuum?
    No LP cut out is fine. When we use the cutout with manifold gauges, it works fine but with these flexible lines, sometimes comp goes into vacuum.

    The cut out seting is set @ 20 PSIG.

  5. #5
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,758
    Rep Power
    46

    Re: LP/HP Connector Lines

    Try changing your gauge line for a temporary larger one.
    And see what happens.
    I like Nike am intrigued to know as to where the suction is connected.
    It is unusual to oil log a suction line?
    Grizzly