    Delay On Timers



    Where shall the delay on timer should go -- before compressor contactor or before liq. line solenoid valve??

    What should be the setting for the timer in case if it is in series with compressor contactor, especially for scroll compressors?

    Thanks in advance!



  2. #2
    Join Date
    Oct 2007
    Location
    NZ
    Posts
    85
    Rep Power
    17

    Re: Delay On Timers

    Quote Originally Posted by jwasir View Post
    Where shall the delay on timer should go -- before compressor contactor or before liq. line solenoid valve??

    What should be the setting for the timer in case if it is in series with compressor contactor, especially for scroll compressors?

    Thanks in advance!
    what sort of system is it on? all our scrolls on pump down dont have any delay , we only have them on systems with no llsv like air con with psc start that needs equalisation before starting

  3. #3
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Delay On Timers

    Most of the smaller compressors are rated for maybe ten starts per hour so a delay timer should be fitted into whatever circuit you have for to control the compressor.

    Either use the control signal from the thermostat or the coil feed to the compressor start contactor.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  4. #4
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,697
    Rep Power
    46

    Re: Delay On Timers

    Quote Originally Posted by Brian_UK View Post
    Most of the smaller compressors are rated for maybe ten starts per hour so a delay timer should be fitted into whatever circuit you have for to control the compressor.

    Either use the control signal from the thermostat or the coil feed to the chiller start contactor.
    Thanks for the info Brian.
    Never really thought about it that much.
    Now I come to think about it. Most controllers have
    a delay on restart or anti recycle setting.
    Or even as you say a settable amount of starts per hour.
    All makes sense now.
    I drove 40mls to a site once, having been called out to attend a chiller that would not run.
    When I got there the duty engineer and myself, went up onto the roof to find said chiller running.
    "what did you do" was my question.
    Well "I pressed the start button and when nothing happened I called you out".
    " Oh! You never thought to wait the 2 Min's for the anti start timer to time out" said I!
    (Prat!!!)
    And I drove the 40mls back home. (missed my family barbecue as well) coz it was Sunday afternoon.
    Grizzly

  5. #5
    Join Date
    Apr 2006
    Location
    UK
    Age
    55
    Posts
    1,908
    Rep Power
    30

    Re: Delay On Timers

    Quote Originally Posted by Grizzly View Post
    I drove 40mls to a site once, having been called out to attend a chiller that would not run.
    When I got there the duty engineer and myself, went up onto the roof to find said chiller running.
    "what did you do" was my question.
    Well "I pressed the start button and when nothing happened I called you out".
    " Oh! You never thought to wait the 2 Min's for the anti start timer to time out" said I!
    (Prat!!!)
    And I drove the 40mls back home. (missed my family barbecue as well) coz it was Sunday afternoon.
    Grizzly
    Grizzly

    Used to do alot of transport years ago & you would not believe the amount of call outs i have attended where they say the unit will not run.

    Get there & find the unit switched to standby mode (electric) instead of road (diesel)

    Never complained though as always booked minimum of 4 hours and often did less than 2 with travel.
    Last edited by chillerman2006; 08-02-2009 at 08:28 PM.

  6. #6
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,697
    Rep Power
    46

    Re: Delay On Timers

    Never complained though as always booked minimum of 4 hours and often did less than 2 with travel.
    You weren't working for my company then!
    To be fair they have just introduced the 4hr minimum call out.
    Trouble is covering Somerset, Devon and Cornwall means that you often exceed this.
    Just in travel time alone.
    Grizzly

  7. #7
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Delay On Timers

    It amzes me sometimes with "modern" equipment and the fact that the compressor is not protected in this fashion.

    Have a site with Denco close control units and in a short space of time it lost two compressors.

    The electronic controls are the sort that ramp up a control signal in percentages and when it reaches say 60% it send a go signal to the compressor.

    Trouble is being a ramping signal it can also ramp downwards, which these tend to do. Drops to 58% and switches off the compressor. 30 seconds later it hits 60% and away it goes again.
    Simple task to fit some start delay timers into the compressor circuit with a six minute delay. No cooked compressors any more.

    But why didn't the manufacturers fit them in the first place ?
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  8. #8
    Join Date
    Apr 2006
    Location
    Canada
    Age
    53
    Posts
    154
    Rep Power
    18

    Re: Delay On Timers

    Sorry Guys!

    My Question still stays, where shall the delay on timer should go -- before compressor contactor or before liq. line solenoid valve.

    I've seen that if soln stays open and timer delays the compr start, liquid sits on the head and try to break the comp, at start-up.

    Also, if delay is long, scrolls try to move slowly, when ref passes thru it...

  9. #9
    Join Date
    Jun 2008
    Location
    India
    Age
    56
    Posts
    64
    Rep Power
    16

    Re: Delay On Timers

    Jwasir,

    If your system does not have a pumpdown cycle and you are simply switching off the liquid line solenoid and compressor whenever the thermostat setting is satisfied: In this case, the delay timer can energise both the compressor and liquid solenoid together, say after 3 minutes - when the thermostat reset point is reached.

    If you have pumpdown logic, take care of too much cycling of compressor on LP cutout and oil loss from compressor. The energising logic of compressor & sol valve on delay timer could remain same

  10. #10
    Join Date
    Apr 2010
    Location
    Hudds
    Age
    50
    Posts
    75
    Rep Power
    15

    Re: Delay On Timers

    Quote Originally Posted by Brian_UK View Post
    It amzes me sometimes with "modern" equipment and the fact that the compressor is not protected in this fashion.

    Have a site with Denco close control units and in a short space of time it lost two compressors.

    The electronic controls are the sort that ramp up a control signal in percentages and when it reaches say 60% it send a go signal to the compressor.

    Trouble is being a ramping signal it can also ramp downwards, which these tend to do. Drops to 58% and switches off the compressor. 30 seconds later it hits 60% and away it goes again.
    Simple task to fit some start delay timers into the compressor circuit with a six minute delay. No cooked compressors any more.

    But why didn't the manufacturers fit them in the first place ?

    Just out of interest how modern is you equipment, our latest controller has a 6 min delay to stop short cycling.

    This controller has been used for the last 4 years.

    Rob

Similar Threads

  1. Delay on Timers
    By Feeze in forum Electrical
    Replies: 27
    Last Post: 14-10-2009, 09:20 PM
  2. Grazzlin timers
    By dunny123 in forum Electrical
    Replies: 8
    Last Post: 20-08-2008, 02:12 PM
  3. Bigatti defrost timers.
    By Temprite in forum Commercial
    Replies: 6
    Last Post: 22-09-2007, 06:56 AM
  4. Delay Timer
    By Abe in forum Electrical
    Replies: 10
    Last Post: 21-10-2005, 10:17 AM
  5. Time delay for multi compressors
    By iceman007 in forum Air Conditioning
    Replies: 5
    Last Post: 06-11-2004, 08:05 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •