    Exclamation seting super heat



    hey guys i am a new refrigdie just out of trade school and i just did my first call room unit change over evap and condenser and i need some help setting the tx valve super heat settings i have not worked much with tx valves i mainly deal with domestic stuff but the unit is the right size and when every thing is runnig fine it is ok i had a fue problems with leaks on the liqude like flare nut on the tx valve once i fixed that every thing was fine other then i then the evap was not fully frosted if i put more gas in it the peshers would not have been right so i ajusted the tx valve but know i think i have gone to far because the just rang back in said it is fluding back to the compress so how do i set the super heat please help thanks guys the unit is running on r404 medium temp



  2. #2
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: seting super heat

    What is TXV model #?

    Also, read this thread!

  3. #3
    Join Date
    Dec 2008
    Location
    austrailia torquay vic
    Posts
    13
    Rep Power
    0

    Re: seting super heat

    not shore sorry i know i is the small danfoss mechanical with number 01 orifice

  4. #4
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: seting super heat

    Quote Originally Posted by citytosurf View Post
    not shore sorry i know i is the small danfoss mechanical with number 01 orifice
    What is design evaporation temperature and cooling capacity of evaporator?

  5. #5
    Join Date
    Dec 2008
    Location
    austrailia torquay vic
    Posts
    13
    Rep Power
    0

    Re: seting super heat

    1500watts design temp of the evap-6

  6. #6
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: seting super heat

    Quote Originally Posted by citytosurf View Post
    1500watts design temp of the evap-6
    Then it is TS2 or TES2 if with external equalization.
    Turn the adjustment screw counterclockwise until the end and then turn clockwise 3 turns (3x360°) if it is not Mop charge and 2 turns (2x360°) if it is Mop charge, to restore factory setting.
    Then proceed with subcooling measurements to establish correct charge.

  7. #7
    Join Date
    Dec 2008
    Location
    austrailia torquay vic
    Posts
    13
    Rep Power
    0

    Re: seting super heat

    what should the super heat be set to i think it is a ts2

  8. #8
    Join Date
    Dec 2008
    Location
    austrailia torquay vic
    Posts
    13
    Rep Power
    0

    Re: seting super heat

    it is a internal valve with flare nuts

  9. #9
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: seting super heat

    Quote Originally Posted by citytosurf View Post
    what should the super heat be set to i think it is a ts2
    Do not attempt to change superheat (other than I just told you) until you have correct charge, and cold room at or near design temperature.
    When you readjust valve as I described, you will be having factory adjusted superheat. That superheat could be case, only if you have liquid only at entrance of TXV and cold room temperature near design conditions. In all other cases, you will be having higher superheat, no matter what superheat is adjusted at TXV.

    Keep reading that thread i linked.
    Last edited by nike123; 04-02-2009 at 01:21 PM.

  10. #10
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: seting super heat

    Quote Originally Posted by citytosurf View Post
    what should the super heat be set to i think it is a ts2
    Factory set superheat (also right one for your application) is 5K and it is adjusted as I just told you.

    http://rc.danfoss.com/TechnicalInfo/...1/ri1ae300.pdf

  11. #11
    Join Date
    Dec 2008
    Location
    austrailia torquay vic
    Posts
    13
    Rep Power
    0

    Re: seting super heat

    thanks alot for your help how menny degree td would you run between the evap and the food i wanna get the room sitting at about 1 or 2 dregrees what should my suction presher be around hey while i have got you what should i set my hp lp at i all ready have a t/stat that is the main contorl the hp lp is mainly for safty i was not shore where to set it

  12. #12
    Join Date
    Dec 2008
    Location
    austrailia torquay vic
    Posts
    13
    Rep Power
    0

    Re: seting super heat

    what does mop stand for

  13. #13
    Join Date
    Jan 2009
    Location
    Queensland
    Age
    64
    Posts
    113
    Rep Power
    16

    Re: seting super heat

    maximum outlet pressure.
    Try hitting F7 before you post city.

  14. #14
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: seting super heat

    Quote Originally Posted by citytosurf View Post
    thanks alot for your help how menny degree td would you run between the evap and the food i wanna get the room sitting at about 1 or 2 dregrees what should my suction presher be around hey while i have got you what should i set my hp lp at i all ready have a t/stat that is the main contorl the hp lp is mainly for safty i was not shore where to set it
    Please format your sentences, it is hard to read without any formatting.


    TD depend on evaporator construction and application. For your case it is important to know what humidity you want in cold room.
    Pressure in evaporator is result of evaporator air in temperature and TD of evaporator. TD of evaporator could be adjusted with superheat change and air quantity at evaporator.
    You need to ensure enough total superheat (evaporator superheat+ suction line superheat) to ensure that liquid cannot come to compressor. In the same time high evaporator superheat mean low humidity and inefficient evaporator.

  15. #15
    Join Date
    Dec 2008
    Location
    austrailia torquay vic
    Posts
    13
    Rep Power
    0

    Re: seting super heat

    the room is at a restaurant. They have meat and vegetables in the room

  16. #16
    Join Date
    Jan 2009
    Location
    Queensland
    Age
    64
    Posts
    113
    Rep Power
    16

    Re: seting super heat

    Here city, download this and have a read. The units are all imperial but the info is good.

    Ah, that's better. We can understand that.

  17. #17
    Join Date
    Dec 2008
    Location
    austrailia torquay vic
    Posts
    13
    Rep Power
    0

    Re: seting super heat

    thanks alot that was a good help

  18. #18
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: seting super heat

    Quote Originally Posted by citytosurf View Post
    the room is at a restaurant. They have meat and vegetables in the room
    Than best is to have high humidity which mean low TD of about 5K.

    That mean 2°C room temperature - 5K TD = -3°C evaporation temperature (4,5 Bar gauge) but only when room temperature is 2°C and TD of evaporator is 5K
    Last edited by nike123; 04-02-2009 at 02:34 PM.

  19. #19
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: seting super heat

    Quote Originally Posted by citytosurf View Post
    what should i set my hp lp at i all ready have a t/stat that is the main contorl the hp lp is mainly for safty i was not shore where to set it
    It should be set in way that pressure/temperature newer goes out of operation envelope of compressor.
    For example, if operation envelope of compressor is -20°C/45°C than Lp should be set 4 bar gauge (cut out) and 1bar differential, and Hp should be set 21,5 bar gauge.

  20. #20
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: seting super heat

    I don't want to start a war, but......

    We have experienced fridge engineers emigrating to Auz that have to go back to college, study and then take exams before they are allowed to work in the Auz trade, (if they can get a place in college) and here we have a fellow, just out of college in Auz,(I assume a native of Auz) who doesn't appear to have even the basic understanding of the trade??

    Am I missing something??

  21. #21
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: seting super heat

    [quote=frank;134414]I don't want to start a war, but......

    We have experienced fridge engineers emigrating to Auz that have to go back to college, study and then take exams before they are allowed to work in the Auz trade, (if they can get a place in college) and here we have a fellow, just out of college in Auz,(I assume a native of Auz) who doesn't appear to have even the basic understanding of the trade??


    Nobody forbid immigrants that, after exam, forget everything they knew.

  22. #22
    Join Date
    Jan 2009
    Location
    Queensland
    Age
    64
    Posts
    113
    Rep Power
    16

    Re: seting super heat

    Quote Originally Posted by frank View Post
    I don't want to start a war, but......

    We have experienced fridge engineers emigrating to Auz that have to go back to college, study and then take exams before they are allowed to work in the Auz trade, (if they can get a place in college) and here we have a fellow, just out of college in Auz,(I assume a native of Auz) who doesn't appear to have even the basic understanding of the trade??

    Am I missing something??
    He's from Victoria Frank. We make allowances for them.
    We've just exported one of our X apprentices to Scotland. The stories he's sent back from there would turn my hair white... If I still had some

Similar Threads

  1. Capacity control
    By sparrow in forum Training
    Replies: 44
    Last Post: 18-01-2010, 07:49 PM
  2. Replies: 5
    Last Post: 14-09-2009, 07:33 AM
  3. low super heat
    By mgtet in forum Air Conditioning
    Replies: 9
    Last Post: 30-08-2008, 02:00 AM
  4. frostles heat pump
    By Lc_shi in forum New Technologies
    Replies: 27
    Last Post: 31-03-2008, 07:53 AM
  5. Help Super Heat / Subcool?
    By 2aces in forum Air Conditioning
    Replies: 2
    Last Post: 12-11-2007, 11:28 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •